9kw deep fryer, a cooker switch, stop working every few months,
I found the fryer use thin flex cable (see picture 3), it was burnt, the power supply cable are much thicker and it has no problem.
The fryer thin flex cable was just plugged into the switch, no lug,
Am I right? I guess it can be the thin copper flex cable are not contacted properly with the switch, that's why it overheated,
If I soldering the thin flex cable or use a lug ( see pic), it can improved?

Many thanks

lug.jpg

burnt wire.jpg

flex cable.png
 

Attachments

  • 45a switch and socket.png
    45a switch and socket.png
    182.5 KB · Views: 47
What size is the fryer flex?
Unless the connection was badly made or the flex is too small, it is likely that the heat is coming from the switch contacts and the heavy supply cable did a better job of conducting it away.
Ferrules might help to make a better connection to the flex. Do not solder (tin) the end, this makes it look neat but causes a bad connection as the solder is soft and creeps out leaving the terminal loose.
Consider using a better, heavier duty switch, that is not run so close to its maximum rating.
 
  • Like
Reactions: lugluglug
Have you removed the damaged section of cable each time and made the connections to good clean copper?

If you've been connecting to the heat damaged cable each time then that will be causing the overheating of the new switch terminals.
 
What size is the fryer flex?
Unless the connection was badly made or the flex is too small, it is likely that the heat is coming from the switch contacts and the heavy supply cable did a better job of conducting it away.
Ferrules might help to make a better connection to the flex. Do not solder (tin) the end, this makes it look neat but causes a bad connection as the solder is soft and creeps out leaving the terminal loose.
Consider using a better, heavier duty switch, that is not run so close to its maximum rating.
Thanks for your advice, the flex cable from fryer is not small, it could be about 3mm, I will try ferrules then.
 
Have you removed the damaged section of cable each time and made the connections to good clean copper?

If you've been connecting to the heat damaged cable each time then that will be causing the overheating of the new switch terminals.
Sure, good advice, this has been done by others, but today I was helping, and I cut off some burnt cable, the flex cable copper wire are dark instead of copper colour now, but the cable was not long enough, so next time I will try to drag the cable and redo it.
 
Sure, good advice, this has been done by others, but today I was helping, and I cut off some burnt cable, the flex cable copper wire are dark instead of copper colour now, but the cable was not long enough, so next time I will try to drag the cable and redo it.

If it is dark and not copper coloured then you are likely to have made a poor connection and created another fire risk.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
switch burnt every few months
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
lugluglug,
Last reply from
lugluglug,
Replies
6
Views
1,409

Advert