Customer has a 25mm sub main fed into DP isolator (as pictured) then 16mm T&E out of the top to feed 2nd consumer unit about 20m away. 2nd consumer unit has 8 circuits. (1 32A Ring, 2 socket radials, 1 lights, Shower (pump fed no heater), Immersion heater, 2 Ovens). Diversity & cable rating aside surely the supply to the 2nd CU should be 16mm CPC as per OSG 4.4 not 6mm?
  • Is the 6mm earth conductor supply to the 2nd CU classed as "the" earthing conductor? If so surely OSG 4.4 applies (16/16)
  • or is it considered as the main protective bonding conductor in which case 6mm is still inadequate for 16mm live conductor supply isn't it? (16/10)

If the earthing conductor is inadequate do I run a 10mm earth cable alongside the run? Or rip it all out and use 20m of "proper 16mm L,N,E tails"
Thanks in advance
 
get a pefc reading at the 2nd CU. then use the adiabatic to see if that 6mm is compliant.
 
  • Like
Reactions: 2 people
get a pefc reading at the 2nd CU. then use the adiabatic to see if that 6mm is compliant.

S= (SQRT(I2*T))/K I=1045.45 T=0.4 K=115
S=5.75mm
Presumably the disconnection time is 0.4s

Thanks telectrix. Just as well the Ze was 0.22 and not 0.2 then!

Does OSG 4.4(i) not apply here then?
 
why use 0.4 secs for the value of t? bet that OCPD will dis. in 0.1 secs or less with a PEFC of 1kA.
 
  • Like
Reactions: 1 person
You say the 25mm is fed into the DP isolater (looks like a 100A main switch), but what is the breaker to the right of that, is it doing anything?

Cant quite work out if there is any OCPD apart from the main cut out for the 20m of 16mm?
 
i would have thogh that that MCB would be 63A if protecting 16mm.
 
And like you said Tel, I 'think' the disconnection time would be 0.1s at that Ze from Fig 3A4

Have to admit I always get a bit confused when I see that straight line on the disconnection time graphs! For the type B breakers (Fig 3A4) it goes straight at just over 10 seconds. For any PFC over that it states 'refer to manufacturers let through data'.

Also the table to the right of that graph shows the fault current required for disconnection time 0.1s-5s, thats quite a big spread. How do we narrow it down and get to this 0.1s figure?
 
ps... Have scoured the forum a bit and anything after the straight line is 'instantaneous disconnection'. Sorry for hijacking the thread a bit Leigh although slightly on topic!
 
i can't understand that table that the IET have put there. if a certain fault current causes disconnection within 0.1 secs, why state 0.1 - 5?
 
Blimey Tel! If you don't know there's not a chance I will!
 
  • Like
Reactions: 1 person
I'm observing the 'be nice' rule here!
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
16mm T&E used as supply to 2nd CU
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
LeighSawczyn,
Last reply from
dingledong,
Replies
13
Views
2,530

Advert