Gavin John Hyde
Patron
Jun 4, 2017
3,806
5,856
12,688
Somerset
www.sulis-electrical.co.uk
Business Name
Sulis Electrical Services Ltd
Got a customer with a 3 phase looped cut out. Only use one of the phases and there is likely a second fuse on the adjacent holder/phase.
I have asked the DNO to take a look and advise as the customer wants an EV charger. With a looped supply you should get dnos advise first. ENA guidance also says assume 60 amps until proven otherwise. So a few things to check here. On a previous job they changed the cutout as it was looped and old. Another they said carry on but fit a ct clamp to limit the load but they did change fuse from 60 to 80 amps whilst there.
Could be the 3rd fuse holder is supplying next door as its a semi and the whole street is looped supplies.
Did knock to enquire but got no answer.
Likewise could be empty / unused phase.
What are people's thoughts? Don't tend to see many like this in Bath with your main fuse in the neighbours house! Have come across some in the kingswood / hanham areas of Bristol and South Gloucestershire.
I have came across them from time to time.
That's looped in from one property to the next. save on cable.
Reactions: Gavin John Hyde
Is it looped via one of the fuses, or just feed cable in/out to next door with another fuse cut-out (as it appears in photo)?
I would say it is likely the other cable is not fused, and only the centre fuse is being used. The fused terminals are on the top of the cutout.
Prob be looped to next door and the blank unused ways are not connected in the head
will be single phase in there
Or you may find one has a fuse or solid link for next door
Suggest a DNO visit
Suggest a DNO visit
Have arranged just that. Need to confirm they are happy for the charger to be connected with it being a looped supply of some sort. Also unsure on next doors connection to this.
They can then tell me if the fuse can be changed to 100 amp of if its a ct clamp pod Point job or zappi to limit the max demand in the house with charger fitted.
Your western power over there so good luck on that one way forward is as above but I would go Pod Point :)
Looks like it’s looped on the supply side.
Row of houses.... first house comes off L1, second from L2, 3rd from L3....
You’ll find every house has same 3ph head but only one fuse will be used. (The other fuseholders may have nothing in them)
Each house gets a single phase installation.
Fairly simple way to get free leccy for the weed farm. :eek: :oops:o_O
I'm on good terms with the local DNO office, often have them out doing bits, don't always charge either.
Gavin John Hyde
Patron
Somerset
Website
http://www.sulis-electrical.co.uk
Business Name
3 phase looped service cut out
Gavin John Hyde,
Gavin John Hyde,