Discuss 3 phase socket in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi I have a 3 phase socket to change like for like does anyone know what tests have to be carried out after
Yes continuity of cpc. Phase sequence, IR, Zs, polarity. Can't think at the moment Dinner is immanent.
All of the above AND continuity of the N if it is a 5 pin socket.
Some equipment can be destroyed by loss of N
The fundamental tests you should do are insulation resistance, earth continuity, Zs and rcd test if applicable. These should be recorded and submitted to the client maybe on a Minor Works Certificate.
@Alan-b welcome to the forum, but with this one it's probably best you get a sparks with the test equipment and experience to do this. It's just with three phase, the bang is a lot bigger and the fireworks more spectacular, if you get it wrong. All being in order, it's a half hour job.
Reply to 3 phase socket in the Industrial Electricians' Talk area at ElectriciansForums.net
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Hi I have UPS 50KVA and the inverter output AC voltage is feeding a distribution panel 120/208 V 4 wires when I check UPS display it shows me...