Hi all,
Company I work for have moved into a new factory and asked me to wire up the work benches, properly this time as before they just used a selection of extension leads dragged across the floor.
Anyway. On the wall there is a 4 core 6mm SWA cable terminated into a rotary isolator fed from a 3 phase 32a MCB.
Am I right in thinking that I can fit a TPN sub board in place of the isolator and then run 3 radials out to supply the benches?
One guy I work with said to just take 3 circuits off the existing cable in a junction box and share the neutral between them but I don't like the sound of that. Segregation of circuits and all.
Basically I want to use the 6mm 4 core as a distribution circuit to feed 3 x 20 radials, 3 x 32 rings if possible. I'm just unsure as the loads will be slightly unbalanced depending on what the guys are working on. I'm trying to save running 3 x 2.5 / 4 mm 3 core SWAs from the main distribution board because it's a fair distance away. Load on each phase would realistically only ever hit 10amps and am I correct in saying that the 6mm cable is good for approximately 32 amps per phase?
Does this sound acceptable to you guys? I rang the NICEIC tech helpline and the guy wasn't really sure what I was getting at.
Thanks in advance.
Rich
Company I work for have moved into a new factory and asked me to wire up the work benches, properly this time as before they just used a selection of extension leads dragged across the floor.
Anyway. On the wall there is a 4 core 6mm SWA cable terminated into a rotary isolator fed from a 3 phase 32a MCB.
Am I right in thinking that I can fit a TPN sub board in place of the isolator and then run 3 radials out to supply the benches?
One guy I work with said to just take 3 circuits off the existing cable in a junction box and share the neutral between them but I don't like the sound of that. Segregation of circuits and all.
Basically I want to use the 6mm 4 core as a distribution circuit to feed 3 x 20 radials, 3 x 32 rings if possible. I'm just unsure as the loads will be slightly unbalanced depending on what the guys are working on. I'm trying to save running 3 x 2.5 / 4 mm 3 core SWAs from the main distribution board because it's a fair distance away. Load on each phase would realistically only ever hit 10amps and am I correct in saying that the 6mm cable is good for approximately 32 amps per phase?
Does this sound acceptable to you guys? I rang the NICEIC tech helpline and the guy wasn't really sure what I was getting at.
Thanks in advance.
Rich