You will be installing a sub-main from the cellar to the flat, this is a distribution circuit which you may not have come across before if your work is purely domestic.

I apologise now if I am teaching you to suck eggs here but from what you have posted so far I think this may help.

A sub main is in principle no different to a radial circuit which feeds a single point, such as an immersion heater supply or cooker supply, but usually a bit bigger.

You will need to establish how big a supply you need to the flat using diversity calculations and a bit of common sense.
You can then select a suitable sized sub-main.
I'll be surprised if you need more than 40A but personally would run a 63A supply minimum to allow for any future increase in load (eg replace gas cooker with electric)

Then you can carry out the cable size calculations as per usual.

It is advisable to use a switchfuse with bs88 fuse rather than an MCB for the OCPD.

You could use T&E cable but SWA is far more advisable, it will negate any need for an RCD on the submain. Also the cpc in large T&E will likely be too small, especially if main bonding is required. 3 core SWA will obviously give you a bonding conductor in the cable without having to run a seperate one. If no bonding requirement then 2core SWA will likely be fine.

The idiots that changed board that was feeding a door access panel backed up the bs88 fuse inside the panel with an mcb etc.

This meant that instead of blowing just the local bs88 it tripped the mcb as well plunging the patients into darkness
 
Where has anyone mentioned putting a meter at the other end if the submain?
He as asked about running a submain from the new meter in the cellar.
As an alternative he suggested having the DNO install the meter in the flat so that he would not need a submain.
 
Where has anyone mentioned putting a meter at the other end if the submain?
He as asked about running a submain from the new meter in the cellar.
As an alternative he suggested having the DNO install the meter in the flat so that he would not need a submain.

People seem to be getting confused.

best option is have a meter for each flat next to intake.

Then the landlord can have there own put in the flat next to the ccu, this way everyone is happy.

Any one stealing lecky, no problem check the reading on all meters and see which ones don't tally
 
Where has anyone mentioned putting a meter at the other end if the submain?
He as asked about running a submain from the new meter in the cellar.
As an alternative he suggested having the DNO install the meter in the flat so that he would not need a submain.

If I read the op correct, he does not want the meter in the cellar, running a sub will make no difference, unless the DNO run newsupply off the 3phase and fit link fuse to the desired location, sorry if I have got this wrong.
 

Reply to >30m distance from meter to consumer unit. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
422
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
753
I have a doorbell I want to install. The issue is the 16v transformer is designed to sit on a DIN rail. I have a 10 way 17th edition BG Nexus...
Replies
4
Views
906
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...
Replies
2
Views
2K
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
311

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock