Search the forum,
Discuss 3ph + E Zs calculation? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Can anyone tell me how to calculate the zs in a 3ph+E installation as my tester will not give me a reading. I've looked into it and a special loop tester is needed, if this is right?
Thanks Paul
are you sure you know what you mean? to get a zs on a 3 phase system you just test brtween each phase and earth witch is only 230v and record the highest reading no special testers required. if you need to calculate the psc accross the phases then get a zs accross phase and nutural work out the current usins 230v then times it by 1.73205
regards
aj
You may be trying to test three phase and earth with a three lead instrument? If so, both the neutral and earth crocs need to be connected to the earth bar and the line test lead to the phase you are testing and as AJ says record the highest reading of the three phases. Divide 230 by your lowest reading to give you the worst case scenario of prospective earth fault current on one phase and multiply it by 1.73205 (square root of 3) to give the phase to phase value of PSCC.
I use the same tester and when this doesn't work I normally get ERR5 when the earth and neutral are not connected at the secondary side of the transformer or the earth is not connected at all! You should check this.
Bascially there a set of large floods for a sports pitch that have been imported from America. I was testing from the isolator with lights turned off, should i test with the isolator on? This will put power to transformer on pole.
You need the supply on to perform a loop test and loads should be removed. The fluke 1652 does not like doing earth loop impedance tests on circuits under load, whereas the old robins would do it.
The circuit must be energised to perform the loop test with loads removed. The Fluke 1652 sometime won't test circuits under load conditions.
One to remember is that the Fluke 1652 will not loop test 110v circuits, you will require a special tester for this. I'm assuming that the American lighting is 110v.
Would be a very good idea to switch on the isolator as if not the is no power to do a Zs test.
My head was completly fried on this one, i had all of it set up right borrowed another fluke tester and it worked fine. So my tester is obviously broken, and it's not long been in for calabration. Cheers for all the help guys
Reply to 3ph + E Zs calculation? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Hello Everyone -- So, I am looking to buy a used 5HP 3PH 208 V 10 inch Table saw --- (Motor Plate Data in Image) I am a DIY'er and in...
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...