Customer has himself fitted a new hob of 6.4kw in place of previous gas hob with electric ring x 1 ?
Under the hob there was x 2 sfcu both on there own circuits and both run in 1 x 2.5mm t/e.
He has connected his hob to one of the sfcu fused at 13a and on a 16a MCB at the board.

Using diversity this should do.
However, could he connect both runs of 2.5mm (in theory then 5mm) to a new cooker connection plate and place on 32a mcb covering the max 26.7a of the Hob.
Or is that a No No.
 
as long as the 2 cables are of equal length ( resistance) and follow the same route, then it's parallel conductors and should be OK. however, a 6mm cable with a cooker isolator and dual outlet pl,ate would be more conventional.
 
Somebody asked this same question a few weeks ago, but for installing a shower rather than a cooker. Might be worth searching for it, as there were many replies.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
.
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
.
Business Name
.

Thread Information

Title
6.4kw hob circuit
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
sidekick,
Last reply from
Guitarist,
Replies
2
Views
2,950

Advert