Seems to me that the first set of touching cables would always be warmer (all other things being equal), so I can't understand why it shouldn't be derated slightly relative to the spaced out cables.
What's your point?? What sort of heat increases are you actually talking about here, temperature increases that will affect current ratings, that's just nonsense!!
Are we now saying that the temperature increase of a cable doesnt affect the current rating of the cable??? This is just getting a farce....
Just look at the regs EG table 4E4A. lets take 35mm 4 core cable. How this is installed affects the current rating doesnt it.. The max being 162A (in free air...) the min being 115A (direct in ground or in ducting in the ground...) This is due to the heat dissipation of the cable or temperature.
That is why in parallel cables, if touching (and a couple of other factors) you have to de-rate the cable... Single source supply or multiple supplies, they both need de-rating..
You're talking about installation method, NOT grouping!
Chr!s - wrong sort of maths! Try ignoring the tables and use some trigonometry. The tables aren't designed for this scenario, in fact for certain types of installation methods they are woefully inadequate.
This ive got too see, so we have the "Real Heat" and the "Imaginary Heat"
I'm loosing the will to live, now. FORGET THE SODDING TABLES!! (to a point).
Basic principles -
1) the ability of a cable to radiate heat is proportional to its surface area
.............
and also the temperature gradient of the cable to its surroundings.
So two touching objects, at the same temperature, won't be able to dissipate any energy from the contact area, which will lead to a temperature increase over the rest of the surface area of the objects and arguably a temperature rise in the objects themselves.
and also the temperature gradient of the cable to its surroundings.
So two touching objects, at the same temperature, won't be able to dissipate any energy from the contact area, which will lead to a temperature increase over the rest of the surface area of the objects and arguably a temperature rise in the objects themselves.
As I have been trying to explain all along, with my rubbish english, but you have hit the nail on the head
The wrong nail, though! Even if we say for arguments sake that there is (d) surface area 'not doing a lot' (back to the calculus), it doesn't really matter as we have a much larger (33% ish) surface area to start with!
Right, at this point I'm outta here, something about water and horses springs to mind.
Before you try getting any smarter, you need to read what i actually said again!! What you seem to be talking about, is the current ratings associated with installation method, which is a totally different aspect altogether!!Are we now saying that the temperature increase of a cable doesnt affect the current rating of the cable??? This is just getting a farce....
Just look at the regs EG table 4E4A. lets take 35mm 4 core cable. How this is installed affects the current rating doesnt it.. The max being 162A (in free air...) the min being 115A (direct in ground or in ducting in the ground...) This is due to the heat dissipation of the cable or temperature.
That is why in parallel cables, if touching (and a couple of other factors) you have to de-rate the cable... Single source supply or multiple supplies, they both need de-rating..[/QUOTE]
As i've said a couple of times now, if your fool enough to employ a parallel single circuit, for all the advantages it will give you, and then start applying unwarranted factors, then you get on with it, or better still use the oversize single cable, it makes far more sense to you!!
Couldn't agree more!! It's quite amazing actually!!
They just can't get it through their noggins a parallel single circuit is just that, a single circuit!! It's not the multiple circuits they are trying to make out it is, in order to apply this crazy idea of a grouping factor!! I'll not be saying another word on the subject, until they can explain why they don't apply a grouping factor to a 3 or 4 conductor trefoil run circuit, if all the phases are equally loaded!! lol!! Or if they can show me a regulation from any internationally recognised country codes/regulations that applies a grouping factor to a parallel single circuit!! I spent some time today (foolishly) looking through German, American, and French codes, and found nothing, which was exactly as i expected!! lol!!
Before you try getting any smarter, you need to read what i actually said again!! What you seem to be talking about, is the current ratings associated with installation method, which is a totally different aspect altogether!!
As i've said a couple of times now, if your fool enough to employ a parallel single circuit, for all the advantages it will give you, and then start applying unwarranted factors, then you get on with it, or better still use the oversize single cable, it makes far more sense to you!!
I really apologise if I am coming across like Im trying to be a smart arse.... I dont mean to be... its just the way I phrase things sometimes.... just as the missus!
I would love for you to really explain it to me in my examples. I can same money here, but I cant give a reason why to my bosses as they think, like me, you apply it to both.
It does state in Table 4C1: Rating factors for one circuit or one multicore cable or a group of circuits, or a group of multicore cables.....