Various details missing there, which should not be missing IMO. Namely end to end values on some circuits and R1R2 values. Limitations to the testing is acceptable, but in this instance some important potential issues have not been either deduced or verified to be OK.

I have never completed a inspection and test of a installation without at least one observation being made (in reference to the second picture). Was there a page before the second photo that had any observations perhaps.

Who did the testing - a small or large company or one man band? And of of curiosity how much was paid.

Oh, and the Zs values should be recorded too. Poor.
 
Last edited by a moderator:
  • Like
Reactions: Octopus
Agree very poor eicr,how much Dare I ask
 
5 sec. disconnection time for lights, 0.4 secs. for circuits > 32A. what a plonker.
 
Hello All

local sparks to me, full contractor, this is from the solicitor to my friend buying the house, I said not worth paper written on, he contacted estate agent they mentioned it says satisfactory & client of theirs have paid for the test.
I am now going in Monday to do periodic for property.

I did not show the rest but least I say we have TNCS down but with a figure 0.80 for the ze inquired so says it all
 
5 bed house, not saying impossible but 200M ohms L/N IR testing find hard to believe myself but we shall see I will post up my results when I have done
 
Last edited by a moderator:
That's some bad testing I bet the actual results are nothing like that haha.

Got to love this types of testing, worked for a company before (only as a trainee so working with a sparky) when doing DB upgrades who said just do a Ze and a Zs on sockets and rcd test that's it the supervisor in office will fill in the rest. also if there is a link between lighting which causes rcd to trip just put both lighting on same rcd not even try to find the problem. Safe to say I wasn't there long.
 
Sheeeeet! I knew this would come back and bite me in the arris!
 
testing the above house start of the results just writing up now, just got to edit parts of cert fill in the new blanks have some other pictures will try & post.
also observations page
 
had to remove the undercab light next to cooker switch to undo cooker switch, not a problem to get the reading for the oven circuit, but when I did undo the under cabinet light the load of rubbish fell out that must have been placed there when the person before me tested the same circuit couple of weeks before.
or did they not take the switch of to get their reading?

IMG_0124.JPG

IMG_0123.JPG

IMG_0122.JPG

IMG_0108.JPG
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
a freind buying house this is pereodic report he has I have taken a snip only
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
16

Thread Tags

Advert

Thread statistics

Created
marc8,
Last reply from
ED17,
Replies
16
Views
2,825

Advert