A client is having a new kitchen installed and they have requested 8 new sockets in various places, there are currently 8 sockets installed.

The consumer unit has couple of spare ways and located in the kitchen, also Im installing downlight from below so the ceiling will be no problem to make holes etc.. I could also install majority of the new ring without removing any old units or causing much disruption for the client

I was just after some opinions whether to install a new ring main for the new sockets or just extend the existing ring main circuit. Its a 5 bed detached house and it has two existing rings..sockets up and down & kitchen and utility

All advice greatly appreciated
 
Hi

A client is having a new kitchen installed and they have requested 8 new sockets in various places, there are currently 8 sockets installed.

The consumer unit has couple of spare ways and located in the kitchen, also Im installing downlight from below so the ceiling will be no problem to make holes etc.. I could also install majority of the new ring without removing any old units or causing much disruption for the client

I was just after some opinions whether to install a new ring main for the new sockets or just extend the existing ring main circuit. Its a 5 bed detached house and it has two existing rings..sockets up and down & kitchen and utility

All advice greatly appreciated
32Amp 4mm2 Radial
 
If you install a new ring then it will be notifiable.
I don't really like the idea of having to switch off two breakers to isolate all the kitchen sockets. IMO (depending on the layout and what they are using) one circuit would be better.
 
  • Agree
Reactions: Timbo
Is the kitchen a dedicatd RFC or is it supplying other rooms in the property, is there a spur for garage etc?

I'm with Pete, a 32 amp radial would be simple enough to install.
 
16 double sockets in a kitchen...o_O
 
  • Like
Reactions: westward10
how big is the kitchen , why would you put in a new ring for the new sockets ,extend if possible .
 
  • Agree
Reactions: robd
9 doubles and 7 singles/spurs (for appliances and in cupboards for lighting)
What appliances will there be on these circuits?
 
  • Agree
Reactions: Rpa07
I agree with 123 until we know the appliances that are on the 7 spurs single sockets for working out diversity.
 
  • Agree
Reactions: Rpa07
Find out what is going to be plugged in. Work out what the maximum (although unlikely) current is going to be, then do the maths.
If the existing ring cable (you did say that the kitchen had it's own ring) can support the load then make sure the protective device can protect the cable and simply extend the ring.
I worry sometimes that I over simplify problems.
But it does seem to work.
 
Surely there's only so many appliances you can have in a domestic kitchen, and the existing RFC (kitchen & utility) should just be extended.
 
  • Agree
Reactions: 1 person
Then consider common sense .............. a customer can only use so many appliances / accessories at once

AND go back in time and lots of houses only had 1 socket circuit and that often included the immersion.

Extend what you have.
 
  • Like
Reactions: Midwest
Horses for courses. The kitchen I'm doing at the moment has a ring for general use, along with separate 20a radials for oven, steam oven, boiling water outlet, built in coffee machine, and a 32a radial for dishwasher/vacuum drawer/waste disposal. I'd always try and keep appliances off a kitchen ring simply because it minimises disruption in the event of faults.
 
  • Like
Reactions: Wilko
Horses for courses. The kitchen I'm doing at the moment has a ring for general use, along with separate 20a radials for oven, steam oven, boiling water outlet, built in coffee machine, and a 32a radial for dishwasher/vacuum drawer/waste disposal. I'd always try and keep appliances off a kitchen ring simply because it minimises disruption in the event of faults.

But then that's a different thing, your case, OP case needs to provide more info.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Nottingham

Thread Information

Title
Additional Kitchen ring?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
richo106,
Last reply from
Midwest,
Replies
21
Views
4,837

Advert