I think the point shanky was trying to make was that the conductors could be e.g. twisted together and not even in socket terminals but you'd still get end to end continuity
 
Yes but the point is if you're just carrying out the tests at the CU you're wasting your time because you're doing it wrong. The r1, r2 and rn tests prove that you have a continuous ring, nothing more.
 
you guys dont read the full posts do you? i was saying most people do this test at the board and it only takes one missed socket to hide this issue.

just because it would be very rare to find it doesn't mean we should ignore that it can happen, without knowing what can and cant happen it makes the job a lot harder.

in an ideal world you would spot this kind of problem before you even get your test gear out

its called a test and inspection your supposed to do a visual first and its something to watch out for because things like this might come up as clear during tests but its not right

But the OP hadn't said there was any underlying faults with original install, so the polarity must be correct before he started work. So the fault has been introduced by his workmanship, so he will know where all the sockets and connections he has done so absolutely no excuse for not testing fully.
 
you still haven't elaborated someone else did. maybe you werent reading the posts mate

I have elaborated..... jesus mate what are on on about. Testing at the board proves nothing does it????????? YOU HAVE TO TEST AT EVERY SOCKET TO VERIFY CONTINUITY AND POLARITY NOT JUST AT THE BOARD.
Read post 51
 
Last edited by a moderator:

Reply to Annoying simple circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
821
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
290
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
479
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock