Discuss Benefits of open bus couplers? in the UK Electrical Forum area at ElectriciansForums.net
Evening gents, bored in work this evening so decided to try and get your input on something. We've recently had a new Emergency Care Centre built at my hospital. As you probably know, in hospitals there are 'essential' and 'non-essential' supplies (self explanatory as to why they're called that). The usual set up is as follows..
Example being a ward area..
2 supplies are run to the LV switch room in the ward corridor (This LV switch room usually supplies 4 different wards). One is essential and the other non essential. We supply with an open bus coupler between the two, so that in the event of a fault on either of the supply cables, we can simply isolate the faulty cable and close the bus coupler, as both cables are big enough to cope with the demand of supplying both essential AND non essential.
However, in the new ECC building the system is completly different, and is as follows..
2 supplies are run to the LV switchroom, the bus coupler is closed and the essential breaker is switched off. Meaning that the 'non-essential' supply cable is supplying both 'non-essential' AND essential. Still with me?.. In the event of a fault on the 'non-essential' supply cable, the bus coupler would open circuit and the essential breaker would supply only the 'essential' side of the DB.
Long winded i know. I personally prefer the first set up as i would argue that, say for instance, we lost a phase on the essential cable. We wouldnt know anything about it until the fault on the 'non-essential' supply cable arose, at which point, we would have lost both supplies and we would be so far in the s**t its not worth contemplating!!
I understand that the chances of this actually happening are thousands to one, but needless to say I think all scenarios, or at least most scenarios should be covered!
Apologies if its not the easiest to follow, im hopeless at trying to explain things in text. Lee
I would assume in the case of the new setup the supply will be routinely changed between the 2 cables.
And I would have expected there to be an External generator connection section at the Ward LV .
cables are NOT routinely changed over. There is an external generator, but all the switching for that is done at our main sub. These are sub mains, small switch rooms for local supplies. Lee
Reply to Benefits of open bus couplers? in the UK Electrical Forum area at ElectriciansForums.net
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Background Two weeks ago, lightning struck a tree in our yard. Many circuits tripped and several electronic devices failed. There was a strong...
  • Locked
5K