- Reaction score
- 7,757
one tin of beans the other a can of worms.knows what you're going to find, though!!
Discuss Best first step to remedy bypassed domestic RCD box? in the UK Electrical Forum area at ElectriciansForums.net
we are only guessing without a site visit. an honest appraisal is essential. as an example. i'd come out and spend up to an hour tracing the fault for a max.of ÂŁ75. if not sorted within that time, then a quote would be given.BTW, just to let you know if you look at your Facebook page and click on the website link, it goes off to some American site in Connecticut. HTH.
Yeah, that's what I thought but unfortunately the last three 'free quotes' only resulted in the ÂŁ500 route. Hence me asking about the bypass reversal here.
I wouldn't be prepared to reconnect up again until an Eicr is done.Yeah, a lot on today. Just wondering why nobody seems to be able to answer the original question i.e. if the RCD has been bypassed, why not connect it up again and test that circuit?? - given the old cooker which might have been the reason for the bypassing (by previous electrician) has now been replaced.
If that solves, a lot less than ÂŁ500...
What I can’t figure from that pic, is if there was an issue on one of the circuits, why not just put that in the non RCD side of the board, leaving the rest protected?
That could be done now just as a temporary measure, there are spare ways there.
What a load of rollocks. There are thousands of CU's with a single RCD protecting multiple circuits. Would you want to rip the customer off by changing the CU every time something simple like an oven or hob needed connecting up? What do you mean surge protection where did that come from??I wouldn't be prepared to reconnect up again until an Eicr is done.
Once that's done and if no faults are found yes reconnect up.
However I would want to change the CU as only having one RCD protecting all those circuits is not good design.
And you must now take into consideration circuits design and spread between appropriate number of rcd,s in installation to minimise the loss of too many circuits in the event of a fault.
I definately wouldn't put the new oven and induction hob on same rcd as all those other circuits.
So yes agree with 3 other sparks a new CU. ether an RCD split board or preferably an RCBO board with surge protection.
Surge protection is a whole other discussion.
?? There's only 18 postssee post #15
Thanks, that sounds interesting - shall ask next guy who comes.What I can’t figure from that pic, is if there was an issue on one of the circuits, why not just put that in the non RCD side of the board, leaving the rest protected?
Thanks for the clear advice, understand your points about the CU and not connecting oven and hob on same RCD (those induction hobs seem to be quite power hungry). Also understand the sense of having EICRs done periodically.I wouldn't be prepared to reconnect up again until an Eicr is done.
As a punter though, still feel the need to query why restoring the bypassed 30mA RCCB - to see if the tripping issue no longer happens - is not being considered even as an option?
The house was rewired around 15+ years ago, and the CU is no longer made but is not exactly something out of the Ark - and the RCCB is obviously working, since it kept tripping for the original guy.
So restoring the bypassed cable will IMHO either result in the RCCB tripping again (meaning more investigation of the circuits, obviously) or it not tripping (presumably meaning that removing the old appliance solved the problem).
If NICEIC regulations etc. specifically prohibit this, then fair enough - would not want a spark to compromise and at the end of the day I am always happy to pay for good work especially where it is essential, and am known for usually giving a decent bonus on top.
Not so happy with the type of guys (NICEIC certified as well) who come along for five minutes, don't even bother to take the cover of the CU off and say airily 'right, that'll cost you ÂŁ500 for a wiring test and a new CU'. Smacks too much of just being a nice little earner. And probably encourages a lot of people to just give up and go with an unqualified but more flexible spark, which seems to be happening more often round here.
Thanks, mate - really appreciate the advice which seems sound to me.What you're suggesting, reconnecting the iffy circuit and seeing if the RCD trips, is affectionately known as bang testing round these parts and is quite rightly frowned upon.
As has been suggested, the iffy circuit can be tested and if ok reinstated. It could well have been an appliance fault causing the tripping, who knows though without testing.
You should be able to get an answer easily and cheaply if you employ an electrician to do just that. So don't say "what do you think I need" rather state "I believe there is a fault on this circuit, would like it tested and, if fault free, reinstated on the RCD side of the CU" then"if there is a fault I'd like a price to remedy it and reinstate on the RCD side of the CU"
Ignore the BSer and keep asking until one says "yes sir I can do that for you"
Repairing the fault, in the event there is one, is a bit of an known unknown (Donald Rumsfeld) but should be significantly cheaper than the ÂŁ500 quoted.
I'm in the 'no need to replace the CU' camp.
You don't need a new CU and you probably don't need anything other than new appliances. It will more as likely be a faulty original oven, it's a simple job for a spark to check the circuit in question. There is no problem having the oven and hob on the same RCD or even the same cable as long as it is rated accordingly. Sounds like these "NIC" sparks are just on the make to me.Thanks, mate - really appreciate the advice which seems sound to me.
NOT a cheapskate, and really value good trades people and don't quibble or haggle - but none of the three guys I got (all registered, all big ads in local paper) gave me much confidence. Too slick, too quick to jump to the 'nuclear option' and not keen to really explain things in simple terms.
I'll go your route - and obviously happy to fork out for an EICR for my own piece of mind down the road.
Cheers.
Yeah, I heard that olde Belling type electric ovens can often cause the tripping, so think you might be right there.You don't need a new CU and you probably don't need anything other than new appliances. It will more as likely be a faulty original oven, it's a simple job for a spark to check the circuit in question. There is no problem having the oven and hob on the same RCD or even the same cable as long as it is rated accordingly. Sounds like these "NIC" sparks are just on the make to me.
Yep, given that GET/Schupa aren't made any more and you can only (just about) get spares via eBay, I know that down the line it makes sense to get a new CU - hopefully that manufacturer won't be swallowed up. I'm just not keen on the sparks who make a new CU the first/only option before trying a simpler solution to begin with.I agree you don't need a new cu for the works you are carrying out, but I would recomend it.
It's my opinion, but as the customer the choice is yours and I would carry out works to your requirements if it was within the regs. But I would give you reasons why I would recomend CU.
As I explained in earlier post that sparks burnt out commented on its not good design to have too many circuits on one RCD.
Thanks for the info - just realised it might help if I uploaded the front of the CU, showing the (theoretical...) circuit names.Looks to me, that there are two circuits (3 & 4) that have been disconnected.
Also judging by the 6mm2 crimps, it looks like someone has relocated the 2nd RCD protected circuit from the non-RCD side.
Actually only the original unqualified electrician (sent by the kitchen fitter and not a great worker) took the cover off and said this (because he was about to connect up the appliances). The other three qualified electricians were informed by me of the first guy saying there was a bypass - and they just stood there, making no move to take the cover off and actually examine the box, simply quoting an initial job cost.I thought each of the electricians had told you that the RCD had been bypassed - they must have took the cover off to know this.
Reply to Best first step to remedy bypassed domestic RCD box? in the UK Electrical Forum area at ElectriciansForums.net