Would you bond it or not. Getting mixed opinions on it.
No.
If you connect this metal frame to the earthing/bonding arrangements of the entire installation a fault anywhere on the installation may introduce a dangerous potential onto all metal work connected to the system,including the pergola. Within a building this is not an issue because a person is effectively insulated from the general mass of earth by the normally electrically insulating floor.The purpose of bonding is to prevent a PD between conductive and extraneous conductive parts within the building.
Externally a PD on a metal frame would be very dangerous to a person in contact with the frame and the ground,hence IMO bonding the frame increases the shock risk considerably. Neither is it considered a conductive part as it is not part of the electrical installation so earthing it should not be required. It is up to the installer to make sure cables and accessories are installed in a manner which prevents any possibility of a fault to the frame.