Hi ,I have asked 2 electricans had 2 diferent ansewers can anybody help, my inverter works when the resistance ,at the inverter end ofthe cable,is less than 1 ohm, is that value the resistance of just the AC cable between inverter and CU, or the value of AC cable between inverter and CU +the value of resistance from substation to CU
 
R1+R2 is the impedance value of the line and CPC conductors combined of the AC cable between the consumer unit and inverter.

Zs is the impedance value of the distributors external line and return earth path (Ze) combined with R1+R2.

How and where was this 1 ohm measurement taken?
 
Last edited by a moderator:
Hi, my inverter keeps triping out on sunny days,the ohm meter reads 1.2 at the inverter end of the AC cable,my installer say the value is only .8 though as he takes the grid value .4 off the 1.2 ,is this correct
 
Do you know the size of cable? It should be noted on your Electrical Installation Certificate. Also, what's the approximate length?
 
Hi, my inverter keeps triping out on sunny days,the ohm meter reads 1.2 at the inverter end of the AC cable,my installer say the value is only .8 though as he takes the grid value .4 off the 1.2 ,is this correct

Those figures would suggest:

Ze = 0.4ohms
R1+R2 = 0.8ohms
Zs = 1.2ohms

However, you don't calculate Ze by taking the R1+R2 value away from the Zs value. Ze needs to be measured with the installation isolated and all parallel earths removed. You can take this figure and add R1+R2 to get a calculated Zs figure though in reality the actual Zs figure would be lower due to parallel earths like the bonding conductors.
 
mmm sounds like another long run of 2.5!!!!

Yeah, around 41 metres of 2.5/1.5 t&e!

If it is 2.5 t&e and the length is around 41 metres then the same route using 6mm t&e would give an R1+R2 value of 0.43ohms and a Zs of 0.83ohms at the inverter assuming the quoted Ze figure of 0.4ohms is correct.

A lot of this is assumption though until the OP confirms cable size and length.
 
Hi, sorry not got back, internet down, I have a NAPIT ELECTRICAL CERTIFICATE ,is this the cable size,protective bonding conductot 10 mm ,but if that is the cable it is wrong ,it is 6mm 4core twined up so ineffect I been told 12mm.As for the lengh, no sign of it on the certificate but I have measured it ,its 150meters long
 
Please tell me if I am correct,R1+R2= resistance value of AC cable from CU to inverter ,Zs = resistance value at the inverter, Ze = resistance value of the grid.
 
it is 6mm 4core twined up so ineffect I been told 12mm.As for the lengh, no sign of it on the certificate but I have measured it ,its 150meters long

That'll give an approximate R1+R2 value of 0.462ohms, add Ze to that of 0.4ohms which you gave and you have a Zs of 0.862ohms.
 
What size system is it?

For comparison, we have used 25mm cable for a 100m run on a 4kWp system. Some may say this is overkill - until they end up replacing a 150m cable.
 
Last edited by a moderator:

Reply to cable resistance in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
489
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445
Commissioning a busduct. My contractor has installed a 2000amp aluminum Busduct in a 17 floor office tower. The specifications state you should...
Replies
0
Views
494
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
Replies
8
Views
894
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock