If you know that the water is plastic then can you not disconnect your earthing conductor and perform the test as per post 5 and 7'

" ie the water and gas pipes are both connected to the boiler so I would end up also testing the water pipe (which I know is an extraneous part):

Don't think he said water was plastic?
The point I was trying to make was -- if? it isn't extraneous then it doesn't need a main bond...........however lol..........

It will be connected to the main earth via pipes/boiler etc (inside the equi zone) so during fault conditions blah blah it will rise to mains voltage and is sitting there on a nice 'wet' concrete slab attached to a great big metal gas bottle with loads of lush wet grass next to it:).

Same as running a copper pipe to your garden hose really if you think about it lol.
Ahhhh..........rcd will cover that though surely:)
 
As our learned colleagues have stated, give it an IR test between the pipework and the earth point. If greater than 23Kohms bond it, if not leave alone else you could be introducing an earth potential!

Not a caravan man myself but if the bottle is on a concrete base I cant see how it will introduce an 'earth'?
 

Reply to Calor Gas Bonding on a static caravan in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Replies
3
Views
1K
Hi I have a property and the mains supply is a TT system I need to put a temporary static caravan in the garden. The caravan will have a water...
Replies
5
Views
4K
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
Replies
20
Views
6K
Hi guys Does the earth Bonding HAVE to be done at the meter or can it be put on the gas inlet to the boiler in a utility room? Plans have changed...
Replies
4
Views
2K
I'm doing an EICR on a static caravan after being called on to fix to a couple of problems due to loose connections. It's all fine now within...
Replies
4
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock