Discuss Caravan park Earthing in the UK Electrical Forum area at ElectriciansForums.net
Is TNS permitted on caravan site? I always thought you could use as TNS as supply cable then TT each pitch, spark I’m working with says you can use TNS all way through if ZS is acceptable
Here we go.
Just because the supply to the installation is TN-S, doesn’t mean PME conditions do not apply.
It’s why BS7671 states “where PME conditions apply”, rather than saying “where the earthing system is TN-C-S”.
Yes ESQCR does prohibit the use of PME for Caravan pitches.
However it does not prohibit the use of PME for static Caravans or for other permanent structures on Caravan sites.
Here we go.
ESQCR are does NOT allow pme conditions to a static caravan! It does allow it for buildings on parks, not the vans themselves
Here we go.
If it is as you put it ‘A TN-S with PME conditions’ then it is not a TB-S is it?
It is up the the DNO to ensure their supply arrangement is vlear nit for us to go around asking questions.
Regardless, BS7671 is clear that a PME cannot be used.
No, it’s not.
From BS7671 Definitions:
Caravan. A trailer leisure accommodation vehicle, used for touring, designed to meet the requirements for the construction and use of road vehicles (see also definitions of Motor caravan and Leisure accommodation vehicle).
Reply to Caravan park Earthing in the UK Electrical Forum area at ElectriciansForums.net
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
We have started a business building garden rooms/caravans/mobile homes under the caravan act. We have only done one so far and I got an...
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
6K