i=p/u

-
Arms
Reaction score
801
A guy asked me to install supply to 3 ph oven, as its few miles away I looked at same kind in another of shops , and it was installed on 32A breaker on 6mm. Anyway I got the rating plate sent to me by photo and I working out 2.5mm on 16A 3ph breaker, am I missing something... I could be but doubt it.
 

Attachments

  • image.jpg
    235.6 KB · Views: 106
It doesn't ,but has 5 cables on the flex. And other ones I've seen have 3ph isolators so can do either, it's a cusine d France
 
is it 230V 3 phase, though? bloody froggy gear.
 
is it 230V 3 phase, though? bloody froggy gear.

Like many of the domestic ovens these days, there will be an adaptable terminal connection block, that caters for several different supply configurations. This 3 phase 230V requirement, just gets the phases linked out and supplied by a single phase supply, with of course larger conductors!! ...lol!!
 
so, are you saying he should size his cable for 44A, E54?
 
Like many of the domestic ovens these days, there will be an adaptable terminal connection block, that caters for several different supply configurations. This 3 phase 230V requirement, just gets the phases linked out and supplied by a single phase supply, with of course larger conductors!! ...lol!!
As Eng 54 says beware! Many European ovens are specified this way as they sometimes have single and 3 phase supplies available. You must follow the installation instructions depending on installation type and strap link them if you run on a single phase supply.
 
It's no probs to me. As for manuals I'd say maybe still in France . We as sparks should be able to determine supply conductors from that rating plate. Which I work out as 2.5mm on 16A tp breaker. Plenty of 2.5 about where I'd have to go buy 4mm
 
problem is that if it's designed for 230V/3 phase, you won't have that supply and you will need to convert to single phase with a line current of 44A.
 
problem is that if it's designed for 230V/3 phase, you won't have that supply and you will need to convert to single phase with a line current of 44A.


Need to look at the manufactures data, and connection diagram. But these European ovens tend to be suitable for most, if not all, of European voltage bands in one way or another!! lol!!
 

Reply to Circuit design in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
849
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
822
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock