Hi All, Am i correct in saying FP200 230v cable and run parallel, (i.e. on same tray/basket with no divider) with FP200 Cat 5 cable. Reason being FP200 is self segregating? Just want a clear answer please chaps.
ThanksI am not sure prysmian make FP200 Cat 5 cable.
If it is cat5 cable then it would be rated to 50V and would not be suitable for use in the same containment as 230V cables.
ThanksLOL,
I have never seen a FP200 Cat5 cable, cant see the need for a fire resistance network cable.
FP200 is not a "self segregating" cable, its just a fire resistance cable used for fire alarms and central battery EM lighting systems (not to be used on self contained fittings as to many people do).
The voltage going through the FP200 would also need to be established.
LOL,
I have never seen a FP200 Cat5 cable, cant see the need for a fire resistance network cable.
FP200 is not a "self segregating" cable, its just a fire resistance cable used for fire alarms and central battery EM lighting systems (not to be used on self contained fittings as to many people do).
The voltage going through the FP200 would also need to be established.
Correction, cable is made my Draka, and is called FireTuf. Incorporates a foil sheath, braided wrap, and cloth, then red sheath. My mistake it's not FP.Don't think you can get FP200 Cat 5, ohh and voltage don't go through anything, it's the voltage applied
Don't think you can get FP200 Cat 5, ohh and voltage don't go through anything, it's the voltage applied
From BS5839
The circuits of fire alarm systems need to be segregated from the cables of other circuits to minimize any potential for other circuits to cause malfunction of the fire alarm system arising from:
— breakdown of cable insulation of other circuits and/or fire alarm circuits;
— a fire caused by a fault on another circuit;
— electromagnetic interference to any fire alarm circuit as a result of the proximity of another circuit;
— damage resulting from the need for other circuits to be installed in, or removed from, ducts or trunking containing a fire alarm circuit.
In order to facilitate identification of fire alarm circuits, cables should preferably be red in colour, unless another form of colour coding is appropriate. By this means, the possible need for appropriatesegregation can be identified, and there will be less likelihood of inadvertent manual interference with the circuits of fire alarm systems (e.g. during work on other electrical circuits).
Basically fire cables should not be next to any other cable/system.
So what are you using the FP200 cable for??
It's in the specification of the job. I'm sure FP is not limited to Fire Alarm systems ONLY.