Got a job in a school. They require power for their computer suite. There will be approximately 20 PC's The question is due to earth leakage should I install 3 off 2.5mm ring circuits cabled in singles all of 2.5mm with the sockets having twin earth connections and the earths at the DB going to seperate terminals. Or 3 off 4mm radials with the sockets having twin earth connections and there being a second earth cable providing a ring circuit for the earths the earths at the DB going to seperate terminals.
What do you think?

AdieB
 
The last computer room I did I used rings using the 'leapfrog' method, as there were three quite linear cable runs. I used dado trunking and provided a high integrity earth. It works fine. Don't overthink it!
 
As with all circuit designs how much is it going to pull ? I agree it needs splitting but 4mm or a 3 x 2.5 rings all at 32A ? is it pulling that much ?.

As for high integrity earthing arrangements you will need to refer to the BGB page 165,543.7.1 through to 543.7.2.101 and decide how you want to deal with the install, the Green OSG page 77 outlines solutions.

ATB J
 
Got a job in a school. They require power for their computer suite. There will be approximately 20 PC's The question is due to earth leakage should I install 3 off 2.5mm ring circuits cabled in singles all of 2.5mm with the sockets having twin earth connections and the earths at the DB going to seperate terminals. Or 3 off 4mm radials with the sockets having twin earth connections and there being a second earth cable providing a ring circuit for the earths the earths at the DB going to seperate terminals.
What do you think?

AdieB


What is the length of the RFC circuits?

at 500W a PC, 20 Pc are about 10KW,

32A is equivalent to 7.4KW at 230V

I would personally install 2 x RFC circuits @ 2.5mm leap frog equally divided between 10+10 computers, if RFC length is suitable for Volt Drop. and install 2 x High Integrety Earth ring back to seperate terminals at the CU.
 
I take it that these circuits supplying these computers/printers/scanners etc are going to have RCD protection?? If so, then it's the leakage currents that's going to determine how many computers or whatever are going to be supplied by each circuit. Generally i will only supply 5 to 6 workstations per circuit to cater for natural earth leakage currents. So it's not just a matter of load calculation when dealing with IT installations.....
 
Just done a quick test on my power hungry twin disked tower and monitor combined. It's drawing 180W at steady state (after initial boot up) for both monitor and PC. Leakage is around 0.5mA. As Engineer54 has said, it's the leakage that you should use to use to drive the circuit splitting decisions, as that will usually reach tripping threashold before exceeding supply of current on a circuit.
 
If the length/volt drop is short/ok, one 32amp ring without 30mA protection would be fine. Just make sure there is a labelled, 30mA protected socket on hand for the cleaners to plug their vacs into.

I'd probably install 2 rings however to allow for future expansion when the class size gets bigger.

There is no need for RCD protection on IT only circuits. Mark it as a deviation on the EIC.
 

Reply to Computer room ring or radial in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
675
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
303
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
761
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock