I have to do a Condition Report for an old installation. Everything is ok but the installation doesn't have RCD's, even for those circuits required by the 17th Edition. Can I write that the installation is "satisfactory" without RCD's ?
any socket outlets with the potential to be used outside or circuits entering a bathroom where satisfactory supplementary bonding is not present would warrant a c2- making the EICR unsatisfactory.
Not that I do EICR's.. but if OP's installation done to correct regs at the time, surly that will be OK. Would not just a C3 suffice?
Yes quite right, if every house in the country without a modern DB board considered a C2, everyone would have to move out to hotels due to the extreme danger of being in the house pmsl.
Reply to Condition report for the old installations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Hi I always thought installations were safe at the time of instalment etc, the Distribution Boards at my works were installed over ten years back...
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
NICEIC Certification Scheme SPD on old consumer unit?
Under amendment 2 of the BS7671, there is now a requirement to fit an SPD as standard. I am due to install a new outdoor socket circuit on an...