Hi

I am doing a installation of two outdoor sockets

They are going to be positioned next to each other

so what I wanted to do was drill through the wall into one of the sockets then take a coupler of some sort connecting both of the outdoor sockets together to then take the cables to the second socket

negating the need to drill two holes through the customers walls

however I’m struggling to find a straight through coupler that has threading either side so I can attach a lock nut

does anyone know where to find these or if there is any alternatives.

I understand one alternative would be to get two female couplers and a little length of conduit but with them going so close together I thought they may just be a gland or coupler with threading either side that I can use

thank you for your help
 
Hi

I am doing a installation of two outdoor sockets

They are going to be positioned next to each other

so what I wanted to do was drill through the wall into one of the sockets then take a coupler of some sort connecting both of the outdoor sockets together to then take the cables to the second socket

negating the need to drill two holes through the customers walls

however I’m struggling to find a straight through coupler that has threading either side so I can attach a lock nut

does anyone know where to find these or if there is any alternatives.

I understand one alternative would be to get two female couplers and a little length of conduit but with them going so close together I thought they may just be a gland or coupler with threading either side that I can use

thank you for your help
Standard conduit coupler and use 2 Male brass bushes instead of threads and locking rings simples.
 
I'm guessing the OP is working in PVC and AFAIK there is no PVC equivalent of the steel conduit coupler. I often wondered why too, as it looks odd if everything is in PVC except for a steel coupler, and two female adaptors back to back with a stub of conduit to join them is needlessly long and clunky.
 
  • Like
Reactions: DPG
I think he is just going through the wall with a cable and needs a method to couple the sockets together.
 
A method that works with metalclad fittings to get things close together is a long male bush through from one box with a lockring between the two and a female bush and/or lockring in the other box. There are no long PVC bushes either, but a brass bush with a PVC lockring between the fittings would look correct.
 
Out of interest only, are you extending an RFC, or feeding via an FCU?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Conduit coupler with threading on both ends
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Dec1815,
Last reply from
DPG,
Replies
5
Views
1,242

Advert