Hi every one need to move 5 internal meters to outside in cabenits we will be running swa back into property can we connect the swa single cores of the swa direct into the meter or is it best to join in junction box with tails and out of junction box with tails to meter bit confused on this thanks
 
I'd be wanting to connect into a switch fuse for the SWA (you'll need something to protect it). The DNO will have a limit on the length of the tails (usually 3M) that they will allow to be protected by there fuse. Assuming you're talking about 5 individual houses here with separate supplies.
 
Do you also need your own overcurrent

Terminate into this and tails from the meter
Wylex Switchfuse 1 Way 100A by Wylex


Too slow

I
f I was doing the 100 meters sprint against topquark,I would rarely break the tape
icon7.png
 
Last edited:
As the chaps have said 1, it sounds like you'll need additional overcurrent protection due to the length and 2, the DNO wont connect singularly insulated conductors into their meter.
 
they are mobile homes landloads supply we are going to install a switched fused isolator going to take supply into isolator out of this with tails to meter then not sure if regs alow single cores to go into load side of meter or will i be best joing them to tails thanks
 
They will need to be double insulated or enclosed by trunking or something
You could mount a section of metal trunking and mount the meter on top
 
You can get a type of heatshrink that conforms to double insulation, it's slightly thicker than the normal heatshrink sleeving and is XLPE, ( as is all electrical heatshrink sleeving) Not sure what brand name it goes under in the UK though... But isn't the stuff you use in the UK classified as ''sheathed single core'' that you use for exposed meter tails and not as such, double insulated??
 

Reply to connecting into meter with swa in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
394
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
725
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
379
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock