Well, it is an initial verification (hence the Electrical Installation Certificate). BUT the certified work relates ONLY to the replacement of the distribution board (which will be clear in the extent of the installation work undertaken box), and essentially the tests carried out following the inspection are simply to ascertain that the existing circuits are safe to put back into service on the new distribution board. You are not taking ownership of the existing installation. After all you cannot verify the route the wiring takes or any number of other things about the prior installation methods.This is not an Initial Verification and tests can be carried out as if it was a Periodic Inspection in which case it is perfectly acceptable to use the EFLI test as proof for earth continuity.
Earth continuity has been verified with a Zs test. So why are you filling in a box stating R1+R2? You haven't done this test (which is not a criticism) - but why are you filling the box out? That is misleading and serves no purpose.Has been tested by way of EFLI.
I don't recall stating which boxes I fill in, I just agreed that Zs-Ze=R1+R2.Earth continuity has been verified with a Zs test. So why are you filling in a box stating R1+R2? You haven't done this test (which is not a criticism) - but why are you filling the box out? That is misleading and serves no purpose.
It doesn't really. It can verify cpc continuity in an already energised installation which is fair enough. But some people are advocating noting down a reverse engineered value under the dead continuity test boxes which is frankly a nonsense.I don't recall stating which boxes I fill in, I just agreed that Zs-Ze=R1+R2.
It still doesn't explain why you feel the need to fill in a box for something which you are stating that you have not tested and have also stated that you do not need to test. If that is your position then do not fill the box for it in! To do so is both misleading and pointless.
Personally for an RCCB I list the times next to each protected circuit rather than list the RCCB separately on a line of its own. But so long as what you have is clear then I don't have a problem with it being done that way.So, for RCD times, the values go on a line for the RCD and not on the lines for every circuit it protects.
It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.It doesn't really. It can verify cpc continuity in an already energised installation which is fair enough. But some people are advocating noting down a reverse engineered value under the dead continuity test boxes which is frankly a nonsense.
A calculated Zs will err on the side of safety. To reverse engineer the R1+R2 will err on the side of danger. It also serves no purpose when you are verifying cpc continuity on an already energised installation with live (Zs) testing. Filling in a box simply because it exists on the form has no merit when you are excluding dead continuity tests. If you are excluding it then exclude it!It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.
It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.
I may be wrong, (I am new to this). but i thought you could use 250v as long as the results comply with 500v
Joking im not. Zs-Ze does equal R1+R2, its a very popular method of testing and not to mention quicker.
What about when live testing through RCD's, this gives a higher value on your zs reading. This would effect the calculated R1+R2