Hi All,
Please can somebody confirm my thoughts.
I have to install a cooker cct. I have chosen 6mm cable. The load is 8Kw. ie 35amps
My calc involves 10amp +30 % remainder fl + 5amps for the socket,
from Diversity, table 1A OSG 17th edition page 97

ie 10+(30% of 25)+5 amps
10+ 7.5+ 5

Total 22.5 amps, ie OK on 6mm cable
Do you agree please
Thanks
 
looks ok to me , just confirm the installation methods to confirm cable size in clipped direct covered in less than 100 mm insulation or more than 100 mm insulation length of the run voltage drop etc
 
Dont see a problem with that but have a look at page 134 which gives the current carrying capacity for the cables if it is reference method 103 then you would have to use 10mm or you could suggest 10mm to customer then cable would not need to be replaced if cooker was upgraded.

Hope that helps


Chris
 
Last edited by a moderator:
when i was taught diversity you took 10 amps from the design current then find 30% of the remainder ad the 10 amps back on and then add 5 amps if it has a socket on the face plate so if the design current is 35amps -10 = 25amps x 30% =7.5amps +10 +5 =22.5amps

Correct A*

LOL
 

Similar threads

D
Replies
5
Views
2K
Australia
Dazzol2009
D
D
Replies
9
Views
6K
P
E
Replies
5
Views
4K
Australia
Engineer54
E
C
Replies
27
Views
8K
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cooker Circuit and Diversity
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
greeny,
Last reply from
Bromd123,
Replies
5
Views
9,249

Advert