Hi All,
Please can somebody confirm my thoughts.
I have to install a cooker cct. I have chosen 6mm cable. The load is 8Kw. ie 35amps
My calc involves 10amp +30 % remainder fl + 5amps for the socket,
from Diversity, table 1A OSG 17th edition page 97

ie 10+(30% of 25)+5 amps
10+ 7.5+ 5

Total 22.5 amps, ie OK on 6mm cable
Do you agree please
Thanks
 
looks ok to me , just confirm the installation methods to confirm cable size in clipped direct covered in less than 100 mm insulation or more than 100 mm insulation length of the run voltage drop etc
 
Dont see a problem with that but have a look at page 134 which gives the current carrying capacity for the cables if it is reference method 103 then you would have to use 10mm or you could suggest 10mm to customer then cable would not need to be replaced if cooker was upgraded.

Hope that helps


Chris
 
Last edited by a moderator:
when i was taught diversity you took 10 amps from the design current then find 30% of the remainder ad the 10 amps back on and then add 5 amps if it has a socket on the face plate so if the design current is 35amps -10 = 25amps x 30% =7.5amps +10 +5 =22.5amps

Correct A*

LOL
 

Reply to Cooker Circuit and Diversity in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Looking for some advice if possible please! Got one if then jobs that you get roped in to and that’s turned from a quick simple...
Replies
3
Views
3K
Hi I'm looking to buy a new double oven and induction hob to replace my very old ones. The current units are both wired to an double pole cooker...
Replies
1
Views
957
Hi All Just looking for a 2nd opinion on cable sizing / breaker for a old cooker. The customer has had a 'Cooker Engineer' out to advise that...
Replies
7
Views
5K
Hi My consumer unit is located in the garage, the cables are currently clipped to a solid wall above the unit. I am considering putting the...
Replies
18
Views
6K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock