Maybe one or two do learn from a bit of experience...and don't jump in headlong thinking they know it all.

Yes. And I was happy to see that. Fantastic. My other comment was about others not the OP. I think what the OP done was great. I don't understand.
 
Yes. And I was happy to see that. Fantastic. My other comment was about others not the OP. I think what the OP done was great. I don't understand.
never mind. understanding with age you will get. th.jpg
 
I'd have to say thanks too. :stooge_curly:
I've been told it's calculate the design current, select the protective device rating, then the cable ?
 
I'd have to say thanks too. :stooge_curly:
I've been told it's calculate the design current, select the protective device rating, then the cable ?
as long as you get the same answer.
 
will be fine on 4mm. one reason 6mm is more otfen used is that you're more likely to have some on the van.
As I do, if you ask your wholesaler about 4mm not many stock much and to be honest the price difference isn't that much.
 
Assuming your customer is replacing their 2.3kw oven with a new 7.3kw hob - why not get the installation instructions of the new 7.3kw oven and see what the manufacturer recommends, if you install anything less than the manufacturer recommends, you are not covering yourself.
 
Last edited:
Diversity for stats kicking in and out is great but tell my wife that she will never have all the hobs and ovens on at once lol

I for one always allow for the worse that way we are always covered also we also are having more and more split ovens (2No) and hobs in a lot of installs, these ovens require being fed via separate radials as the ovens my be 20/32amps and the hob only 13amp via a socket not off the cooker circuit.
 
Assuming your customer is replacing their 2.3kw oven with a new 7.3kw hob - why not get the installation instructions of the new 7.3kw oven and see what the manufacturer recommends, if you install anything less than the manufacturer recommends, you are not covering yourself.

I'd much prefer to use the 60+ year tried and proved system of cooking appliance diversity, than any manufacturers instructions/recommendations. As stated many times here, for some reason these manufactures work around connected loads, that in many cases, not all of those connected loads can be utilised at once...
 
Diversity for stats kicking in and out is great but tell my wife that she will never have all the hobs and ovens on at once lol

I for one always allow for the worse that way we are always covered also we also are having more and more split ovens (2No) and hobs in a lot of installs, these ovens require being fed via separate radials as the ovens my be 20/32amps and the hob only 13amp via a socket not off the cooker circuit.

I bet there isn't many electric hobs out there that are on a 13A plug top, it's normally the oven that comes with a 13A plug top!! lol!!

Hells bells, what sort of domestic oven would need a 32A supply each??
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
4 mm Cooker circuit 32amp MCB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44

Advert

Thread statistics

Created
ianphilip007,
Last reply from
Paul508,
Replies
44
Views
45,563

Advert