Alot of the hob and cooker manufacturers now stipulate 4mm to wire the cookers in ,from the connection plate that is
 
I have just been asked to look at a new double cooker install, the installer has connected the oven by 6mm to a 45A cooker switch and then connected the switch via 4mm to a socket on a 4mm radial protected by a 32A RCBO. Now I expect the RCBO to suitably protect the circuit but has anyone else seen this setup before?
 
I have just been asked to look at a new double cooker install, the installer has connected the oven by 6mm to a 45A cooker switch and then connected the switch via 4mm to a socket on a 4mm radial protected by a 32A RCBO. Now I expect the RCBO to suitably protect the circuit but has anyone else seen this setup before?
Never. First observation is that it's unlikely it was installed by a conventionally trained electrician.A cooker should have its own circuit. Most countries would require it (can, t speak for UK) And if it is allowed, it is terribly poor design.
. Next obvious question is... Is it unsafe? Well like you I would have to conclude that technically the circuit is protected from overload by the 32 amp rcbo. But this has the potential to be a very heavily loaded circuit and cause inconvenience depending on what other appliances are in circuit.
 
Thank you LastManOnline, it was installed by a B&Q kitchen fitter. It is on the same circuit as a washing machine, a freezer and a kettle so I think using diversity it’s within the scope of the RCBO but I think I will err on the safe side and get an electrician to check it
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
4 mm Cooker circuit 32amp MCB
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
44

Advert

Thread statistics

Created
ianphilip007,
Last reply from
Paul508,
Replies
44
Views
45,563

Advert