Discuss Dimmer switch in one room making lites in another glow when off or pulsate on and off? in the UK Electrical Forum area at ElectriciansForums.net
I wired a house about a year ago, We recently got a call back because the led can trims are glowing when the switch is off. We have figured out that the can trims that glow when their switch is off only glow when the dimmer in and for a different rom is turned on. The led can trims are listed as dimmable and the dimmer is listed as being compatible with led lights. We have used the same can trims with the same dimmers together on multiple different jobs and this is the first problem we’ve had with them. Do any of you know what is going on here?
Justin welcome to the forum and are all the lights that your talking about on the same circuit plus other loads ?
There are two lighting circuits in this house and it is happening on both circuits but not at every dimmer on those circuits. Their are only lighting loads on both of the circuits except for one unused switched outlet on one of them. I’ve opened and redone every box in each circuit and there were not lose neutrals or neutrals of different circuits tied together.
LED lights can glow noticeably in the dark with surprisingly small currents, so it could be capacitive coupling but unless you have quite a lot of common runs for the two circuits it seems unlikely.
Here in the UK the cable typically would have an earth all the way to the light fitting (even if not needed there), is that also the case in the USA? If so a floating earth might be one coupling route.
PC1966 yes we have a earth and it terminates to the light fixture. We have a lot of problems with dimmers over here. I don’t understand why buy LED lights for the brightness then install dimmers. I haven’t found a dimmer yet that works consistently on LEDS. Do y’all have the same problem?
The majority of LED lamps for sale here in the UK are not suitable for dimming, but you can get them rated for dimming. Some companies make dimmers intended for LED use but it all seems a bit of a complication (some can be configured for leading or trailing edge switching, etc, to suit LED type). These are ones I have used and they are generally OK:
But due to the low currents involved I find there is an annoying lag between setting the dimmer and the light responding. Probably less of an issue with any significant LED load, but its irritating on just a couple of small bulbs.
Did you check the earth continuity as well?
Might be worth a try. Here in the UK it is normal practice on a new/repaired circuit to measure the supply + earth impedance at the end (furthest) point to make sure it would clear a fault fast enough. But it is still not uncommon for sections of lighting earth to be floating after some joint goes open, or bad work done, as under most conditions it is not noticed and DIYers tend not to test.
a lot of these problems are caused by 2 way switching ( believe called 3 way in USA). this is because the strappers (travelers) have a voltage on 1 or more conductors inducing a small voltage in another. this causes LEDs to glow when they should be off. a snubber often cures the problem.
Reply to Dimmer switch in one room making lites in another glow when off or pulsate on and off? in the UK Electrical Forum area at ElectriciansForums.net
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
The G4 110V 3W dimmable bulbs I purchased work with a dimmer. I can brighten them and dim them, but when I turn the dimmer off, the LED bulbs...
My son is having a new house built. The electrical wiring is almost complete but a problem has been detected. Some of the rooms LED lights...
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Hey all, I installed two LED SAL double spot lights (with no sensor) and the customer rang and said they are glowing at night when the switch is...
