Hi guys, went to price a job today in a Hostel. When looking at the mains position i was shown to the room containing it and to my horror it is in the showeroom. As you can see from the picture , the Board itself has been boxed in with plywood and has a hasp on it it is 700mm away from the shower (out of zone ). Aparently it used to be a small kitchen that had been converted. No circuits are rcd protected and it is a DB is of steel construction. I tried to advise that it was not right and maybe the room use should be changed again. What do you thinkImage0040.jpgImage0041.jpg
 
Need a bit more here fellow like has the shower got a shower tray. If not the zone is 1.2m. the cupboard is locked so needs a tool (key) for access so may be considered outside the zones. Anyhow all the circuits in the location need to be protected by an 30mA RCD
 
the shower has a tray and it is out of zone 2. There is no rcds as, All supplemetry bonding and main bonding is in place so rcds can be omitted ( unless the shower manufacter calls for it)
 
I would be inclined in a place like that to strongly suggest RCD protection.
also you may have supp bonding in place, but are other circuits mechanically protected in walls? Do cables run in safe zones, judging by the fact there is a CU in a converted bathroom i would say...........

Sent from my GT-I9100 using Tapatalk
 
Sorry jamie-spark but reg 701.411.3.3 requires 30mA for all circuits in the location. The fact that the origin is in the location the circuit not related to the shower room will require RCD
 
The current Regulations require that all circuits of the location require RCD protection.
That will mean the circuit feeding the DB will have to be RCD protected.
There are no exceptions to this requirement for skilled or instructed persons.
 
NmC/Spinlondon
can see what u guys are saying after i read th BRB. I read the fact that supplymentry bonding may be omited if all circuits entering were protected by an rcd and took it as the other way too. I cant for abvious reasons ( protection by seperation of circuits ) put the supply circuit on an rcd as it controls 20 circuits on that floor and even if i change the board and put rcbo's on the outgoing circuits, I will still have the supply cable rcd 30ma protected and there will be no discrimination between the tripping of the supply rcd and the out going ways
 
Is there no special IP rating required for the CU enclosure given the proximity to spray, steam and obviously high humidity?
 

Reply to Distribution board in showeroom in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Replies
10
Views
1K
hi ive got an unused isolator in my airing cupboard that use to run a shower. no longer have has have combi boiler feeding a new shower. the...
Replies
16
Views
1K
Helloo guys, First post, so sorry if this is dreary! I'll try keep it simple... I have a client with a distribution circuit supplying AC...
Replies
4
Views
914
Hi. I'm being tasked with installing an electric shower into a property that was built back in the 1980's. The main consumer unit has only 4 ways...
Replies
2
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock