Hi all. I have my inspection tomo to join NICEIC as a domestic installer.

On my main job to be inspected, a board change, my r1 + r2 doesn't marry up with the Ze and zs. Parrerlel earth path somewhere I guess as r1 + r2 is very low. Does this need to me found to satisfy the nic man or will a knowledge of the situation suffice.

Thanks
 
hold on. do you mean r1+r2 or R1+R2. different things altogether, like market and meerkat. and what was your reading?
 
  • Like
Reactions: 2 people
might just be that you are measuring Zs on no-trip. some MFTs will give a higher reading than the true one, due to only pushing 15mA into the circuit.
 
Hi all. I have my inspection tomo to join NICEIC as a domestic installer.

On my main job to be inspected, a board change, my r1 + r2 doesn't marry up with the Ze and zs. Parrerlel earth path somewhere I guess as r1 + r2 is very low. Does this need to me found to satisfy the nic man or will a knowledge of the situation suffice.

Thanks
Jesus! He won't like that at all, better cancel it asap and sort it out!
 
  • Like
Reactions: 1 person
Sarcasm mr monkey. It is an mft tester on 2 wire no trip. Could be the cause. Just though the boiler is on the ring could explain it.
Yeah sorry mate couldn't resist, its really easy as long as you're competant and can display your testing skills, he probably won't pay too much attention to the anomoly as long as you've got the chocolate hobnobs out :)
Just for future reference its R1+R2, r1 is end to end of live on a ring and r2 is end to end of earth
 
Sarcasm mr monkey. It is an mft tester on 2 wire no trip. Could be the cause. Just though the boiler is on the ring could explain it.


You will never get an accurate reading on 2-wire no-trip!
But, as Megger told me, it doesn't have to be accurate on no-trip, as you have an RCD in circuit :)
 
congrats. and @ guitarist, the meggers give reasonably accurate readings on no trip. i checke mine at home on hi i got 0 95 ohms and on no trip, 1.07
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
domestic installer inspection
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Paul117,
Last reply from
Guitarist,
Replies
10
Views
1,479

Advert