Hi all, I'm just after thoughts on this scenario please.
New extension, and I have installed a new kitchen ring servicing approximately 10 sockets (I have this on a 20A RCBO, but can easily upgrade to a 32A)
I have installed a 6mm feed for an electric hob on its own RCBO, I was told that the double oven was going to be on a plug top so installed an FCU spurred from the ring, the distance of the spur is about 1 metre.
Well.....plans changed as they got a better deal on a different model oven and the one they have purchased is 4800 watts which equates to around 20.8A.
I have installed a switched FCU for the oven in 2.5mm, the distance is around 4 metres to the CU. Here is how I'm thinking I may be able to get around the issue...the 2.5mm is rated to 23A, I could substitute the FCU for a 20A DP switch perhaps? I haven't clamped the oven, but I was thinking with diversity the 2.5mm cable would be sufficient, although it is close I agree.
Obviously, my question is does this sound ok? I realise I should have put a new circuit in, I put my hands up to that. The rest of the circuit will be low loading, there are existing outlets that service a kettle and washing machine.
Thanks for taking the time to read.
New extension, and I have installed a new kitchen ring servicing approximately 10 sockets (I have this on a 20A RCBO, but can easily upgrade to a 32A)
I have installed a 6mm feed for an electric hob on its own RCBO, I was told that the double oven was going to be on a plug top so installed an FCU spurred from the ring, the distance of the spur is about 1 metre.
Well.....plans changed as they got a better deal on a different model oven and the one they have purchased is 4800 watts which equates to around 20.8A.
I have installed a switched FCU for the oven in 2.5mm, the distance is around 4 metres to the CU. Here is how I'm thinking I may be able to get around the issue...the 2.5mm is rated to 23A, I could substitute the FCU for a 20A DP switch perhaps? I haven't clamped the oven, but I was thinking with diversity the 2.5mm cable would be sufficient, although it is close I agree.
Obviously, my question is does this sound ok? I realise I should have put a new circuit in, I put my hands up to that. The rest of the circuit will be low loading, there are existing outlets that service a kettle and washing machine.
Thanks for taking the time to read.