Was it a true ZE test? - (did you remove parallel paths before test?)

If that was a clean ZE reading then you have a poor L - E loop (loose connections dodgy cable etc etc)

Again also you could be getting parallel path on your ZS and the cpc not connected at all.

I assume you did r1 + r2 dead test?
 
It may sound stupid but did you check the connections from MET (if there is a seperate MET) to the CU earth bar?

If it is on every circuit you are getting a breakdown some where between MET and CU

Do you have any pics of the earthing arrangements/connections.
 
it is a tns system and i tested at the db on just the main earth and the sheath of the supply and reading was the same 0.75ohm. the only odd thing about it was there was some damage to the sheath of the supply and the original earth clamp had signs of arcing perhaps a previous fault and a loose clamp but still came up with a ok reading with a new clamp.

asked several electricians i used to work with and non of them could give me answer as what could be causing the high reading.
 
Zs = ( R1+R2) + Ze. as truckster said, could be RCDs/MCBs cocking it up. try taking a Zs reading on the busbars. if that is ridiculously high, you know it's not a problem with the circuits.
 
cheers for that amazing what you forget from you college days such a simple calculation and could i hell think how to do it.

yea il give that a go hopefully that will be all it is, on another note have any of you ever seen damage to the main earth clamp/sheath before from arcing?
 
If you've forgotten such a simple calc what sort of electrical work do you normally do?

As your post indicates you don't normally do domestic work, dare I mention notification to BC & Part P (on the basis you're in E&W)?
 
i assume he means england and wales. part p does not apply in scotland, southern ireland, outer mongolia, kazeckstan, '''''''''''''''
 
I'd test on each side of the rcds to see what if any the difference is. Also your saying that every circuit is around 114 ohms?

Is your tester working properly, as every domestic job i've done, measured Zs values differ quite a bit between say a lighting circuit and a shower or cooker radial
 
it is a tns system and i tested at the db on just the main earth and the sheath of the supply and reading was the same 0.75ohm. the only odd thing about it was there was some damage to the sheath of the supply and the original earth clamp had signs of arcing perhaps a previous fault and a loose clamp but still came up with a ok reading with a new clamp.

asked several electricians i used to work with and non of them could give me answer as what could be causing the high reading.[/QUOT

Who fitted the new clamp and what sort did they fit????
 

Reply to Earh loop problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
448
Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
742
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock