Sorry but where is the requirement that the SWA be insulated at the load end to be found?
Could you also explain how insulating at the load end would prevent the TNC-S earthing being exported to any point where the cable could be penetrated by a metallic object?
 
It's very thought provoking and good to think outside of the norm.

I think that 542.1.3.3 covers the earthing arrangement for the swa with TT at the load end.

Interesting debate.
 
Sorry but where is the requirement that the SWA be insulated at the load end to be found?
Could you also explain how insulating at the load end would prevent the TNC-S earthing being exported to any point where the cable could be penetrated by a metallic object?

It'll be in guidance note 8 if it isn't in the BGB.

It won't be exported whatever you do to it, it is impossible to export an earthing system, unless you've found a way of shipping it to another country?
It can either be extended in to another part if the installation, or it could introduce an unwanted earth potential into part of the installation.

As we have already discussed if the SWA is penetrated by a metal object then the OCPD operates and cuts of the supply. This is a fault condition and not normal operating conditions for the installation.

What danger are you seeing from this metal object penetrating the cable?
 
I think it is rather pointless continuing this discussion.
You are detailing the exact reasons why such a cable should not be connected to the TNC-S earthing, but seem unable to understand why those reasons make the practice unsafe.

I also find this practice of referring to non existing Regulations rather tedious.
 
  • Like
Reactions: 1 person
I think it is rather pointless continuing this discussion.
You are detailing the exact reasons why such a cable should not be connected to the TNC-S earthing, but seem unable to understand why those reasons make the practice unsafe.

I also find this practice of referring to non existing Regulations rather tedious.


Hi Spin,

Just to help my understanding, why doesn't regulation 542.1.3.3 apply here?

I can understand your reasoning for thinking that the swa should be connected to the TT earthing system, but the above regulation clearly states that the swa is connected at the supply end of the cable.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Earth rod and Zs values in farm. Help needed
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
44

Advert

Thread statistics

Created
t01474,
Last reply from
ImpededLoop,
Replies
44
Views
8,821

Advert