Discuss Earthing in the UK Electrical Forum area at ElectriciansForums.net
DNO1981
Hi all
Got a PME with 6mm gas & water
Looking into the board there is 10mm gas & water it's been upgraded to 10mm.
The 6mm from the PME is still in place with the 10mm. Board was upgraded to an RCBO board. What would you do?
I have a pic
Cheers
Do you mean there is 10mm in parallel with old 6mm to both water and gas?
I would just leave it be, unless you suspect the 6mm is a much shorter route than the new 10mm and so might take the majority of fault current.
Thats correct in parallel with each other
Can't see the problem if they are in parallel and the 10mm one is not significantly longer than the 6mm one.