Depends what the Zs readings are at all the socket outletslost continuity on cpc of ring circuit, live and neutral fine all test fine.
C2,C3,FI ?
F1all within permitted values
You love the best practice guides admit it!No it isn't.
I would rather chew on a tramps underpantsYou love the best practice guides admit it!
Got my mouth full can't speak.Ha ha , what's your issue with the best practice guides @westward10 ?
Got my mouth full can't speak.
Depends if it is rcd protected.R2D2 or C3PO
No Westy it's protected by "The Force" Young JediDepends if it is rcd protected.
That is an option if you cannot locate the fault.Why not FI then make ring two 20a radials if space in ccu permits