Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
 
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for live, 2 for neutral & 1 fir the CPC. No earth tag at either end of the SWA so can assume it's not being used as a CPC. Should I put this down as a departure or C3.
The armour should be Earthed. But for the lack of ring continuity on the cpc then I would suggest that this needs to be rectified.
 
  • Like
Reactions: pc1966
If they earth the SWA correctly either end while I'm here wouldn't it just go down as a departure?
 
If a core is being used as the CPC, and they earth the armour, what is the departure?
 
  • Like
Reactions: Risteard
If they earth the SWA correctly either end while I'm here wouldn't it just go down as a departure?

No, you don't record departures on an EICR, that is something that you record on an installation certificate.

An EICR is only concerned with reporting on the suitability for continued use of the installation by recording non-compliances which have a safety implication or that could be changed to improve the safety of the installation.

A ring circuit is required to have a CPC in the form of a ring unless it is formed by a metal covering or enclosure containing all of the conductors of the ring (543.2.9)
So as it is now I'd be inclined towards C3 but if the armour is properly connected at each end (and 543.2.7 has also been complied with) then no code.
 
Thanks that clears that up.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Departure from BS7671 or C3
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
bs7671

Advert

Thread statistics

Created
bennie,
Last reply from
bennie,
Replies
5
Views
1,459

Advert