rattlehead85

I am compiling an EICR on a period style house with wiring dating back to mid 60's. The installation has a fuseboard with 3036 fuses protecting all circuits. The bathroom has neither RCD protection or evident supplementary bonding arrangements although there is a 10mm bond to the main water stopcock. The lighting circuit has a class 2 enclosed light fitting and pull switch + a 230v extractor outside zones. What recommendation code should be attributed to this C2 or C3?
 
I would say C2 dangerous in the case of a fault, since there is no RCD protection in a bathroom with no supplementary bonding.
However you could check continuity between metalwork in the bathroom and if <0.05 ohms consider supplementary bonding to be in place, in which case it would be C3 improvement recommended.
 
Class II means they would have no earth and therefore would be safer than class I with exposed metalwork.

However so long as they are suitable for the environment, especially as they are outside zones, then they would be fine in all cases; outside of zones general wiring rules apply (except for sockets <3m from bath).
They would also be OK (except the pull switch) in zones 1 and 2 so long as they had IP protection to IPX4 or IPX5 if water jets.

What is worrying you about these items?
 
No the items and zoning i'm fine with. It was really just the issue of the lack of bonding to the location and if a c3 departure would be more appropriate seeing as class 2 equipment was in place.
 
I see what you mean, you are thinking that if there is no possibility to touch anything "earthy" then a fault that causes something to become live would not be a problem.
This is approaching a non conducting location, I don't think BS7671 has that allowance for bathrooms because of the increased risk of shock. I probably agree if there is no metal in the bathroom the risk is reduced, however you would have to be able to justify this is you decide in your professional judgment that this is safe.

I would not like to take the risk of effectively classifying it as ignore, which is how C3 is viewed.
Then again it has probably been safely in use for years, just like most of the installations that are around now.
 
Thanks guys for your opinions. I will tend to agree with classifying it as a code 2 as there is no evidence of any 16th edition bonding present with clamps or earthing connections in or even close to the location.
 
To my mind, It should be code C2 for lack of bonding, and code C3 for lack of RCD protection.
These are separate conditions which should be reported on individually and not be lumped together.
 

Reply to EICR departure code for bathroom. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
534
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
First : here are 2 x sockets .What code would you give and why ? 3rd pick you can see rear thermal damage on double socket second : Roof...
Replies
32
Views
3K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
649
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock