Well he ain't doing it proper like is he?Hi guys R1+R2 on a eicr mates tutor on the 2395 course said no need to carry out just zs is enough and on ring just end to end readings what's everyone's thoughts on this
You asked for opinions or thoughts file:///C:/Users/Pete/Downloads/Best-Practice-Guide-4-Issue-4-.pdfWhat you mean proper this is coming from teacher teaching the 2395 said it's a good thing but unnecessary just zs is enough
The Tutor said Zs and end to end tests NO R1+R2 required, or at least that's what I think the OP means. You have to ask yourself, why does the EICR form have slots for R1+R2 if it's not required, odd that Westy.What does he mean just Zs, no other tests on the ring final, not even an end to end check.
Hi guys R1+R2 on a eicr mates tutor on the 2395 course said no need to carry out just zs is enough and on ring just end to end readings what's everyone's thoughts on this
But in real life in the event of a fault parallel paths would be included no?On a ring final circuit, does this mean just measuring r1, rN, r2 - and nothing else? Or does he mean Zs (at every outlet) plus r1, rN, r2?
If you measure Zs rather than (R1+R2), then you are not going to know for sure (R1+R2), you can't just subtract Ze (at least if you want to do it properly, and be sure you aren't including any parallel paths due to bonding etc.).
r1 r2 rn and zs at every accessible pointOn a ring final circuit, does this mean just measuring r1, rN, r2 - and nothing else? Or does he mean Zs (at every outlet) plus r1, rN, r2?
If you measure Zs rather than (R1+R2), then you are not going to know for sure (R1+R2), you can't just subtract Ze (at least if you want to do it properly, and be sure you aren't including any parallel paths due to bonding etc.).
Then again they should have didn't types for dThe Tutor said Zs and end to end tests NO R1+R2 required, or at least that's what I think the OP means. You have to ask yourself, why does the EICR form have slots for R1+R2 if it's not required, odd that Westy.
can you please clarify the reason of R1+R2? Think I'll give nic ring see what they have to sayWell I'm not sure the tutor would pass his 2395 doing it his way!
Just because an installation is energised doesn't mean it is installed to regulations.
I totaly agreeWell I'm not sure the tutor would pass his 2395 doing it his way!
Just because an installation is energised doesn't mean it is installed to regulations.
Then again they should have didn't types for d
can you please clarify the reason of R1+R2? Think I'll give nic ring see what they have to say
Thank you everyone for the feed back I've always done the full test but after hearing this from my mates tutor who's teaching the 2395 and also showed me the tutors old eicr papers where all I see is n/a in the R1+R2 column got me thinking have I been wasiting time
End to end zs rcd ir what he says Is necessaryI can understand the thinking on a radial circuit. The purpose of an earth continuity test is to prove there is a valid fault path before energising. As the circuit is already energised then this is not a required test. As the EICR is to prove safety and that disconnection times are met then a Zs result should suffice.
BUT... The problem exists with ring final circuits that can have a valid earth path but still not have ring continuity.
Also, verification of R1+R2 lets you calculate your Zs to check against your live loop reading.
Get your mate to ask the tutor about RFC testing on a periodic inspection.
That's for new installations. I'll bet during an EICR that the insulation resistance readings between live conductors won't be filled out. There is nothing wrong with "LIM" being inserted in any of those boxes - just agree it with the client beforehand.The R1+R2 and R2 column are all blank although it states one should be entered. No end to ends of ring final conductors, I would say that schedule is incomplete.
... My mate even showed me his tutors eicr which shows he doesn't carry it out saying only needed on new installs only not on eicr as its already energised
The top of the column clearly states one should be listed, not put NA in each box.That's for new installations. I'll bet during an EICR that the insulation resistance readings between live conductors won't be filled out. There is nothing wrong with "LIM" being inserted in any of those boxes - just agree it with the client beforehand.
I think Chris's Vid will answer your question
1983 may be a good idea to ask your mate to ask his Tutor what he thinks of the video.
Thank you everyone for the feed back I've always done the full test but after hearing this from my mates tutor who's teaching the 2395 and also showed me the tutors old eicr papers where all I see is n/a in the R1+R2 column got me thinking have I been wasiting time
The top of the column clearly states one should be listed, not put NA in each box.
Replies to date just go to show how this is interpreted. GN3 guide for me.
But I suspect that a considerable amount of testers don't do full dead tests as part of the eicr.
Just trying to show the OP the correct procedure for testing RFCThat is for testing a new install covered under 2394 not 2395 which is periodic there are diferent requierments, it is down to the tester what test needs to be carried out and agreed with the customer and clearly stated on the cert
You should at least do an end to end test and a figure of eight, this should give a rough indication of the Zs.
That fence they sit on must be well worn.Spoke to the nic he said no two places are the same it's about your feel on the installation if you find there as been alteration then do it if you feel it looks good readings good end to end then it's ok all bout your professional judgement I think I'll carry on doing it the way I have been all test that's involved just bit shocked what some colleges are teaching
Again I would point you to the guidance in Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made. Again, like I said, end-to-end tests on the circuit conductors would seem to be reasonable in these circumstances. Obviously the Zs of all socket outlets should also be verified.However, it doesn't prove any of the above. Only the 3-stage RFC testing procedure can, hence why we do it in the first place.
Carry out an eicr with minimal disruption and dismantling whilst verifying the safety of the installation
( Guidance Note 3 which suggests that a full continuity of ring final circuit conductors test may not be warranted or necessary where records exist for existing ring final circuits and where no alterations to that circuit have been made)
How many domestic eicrs have you done where this paperwork was available AND no alterations were made. Fair enough, I'm new to the game, but I reckon it's not all that often anyway
I do the three step. If you're dismantling for end to end then there's no extra skin off your back to do the other two stepsI agree the less dismantling the better during an eicr but ring final conductors end to end is a must for me, i do not however do the full 3 step ring final tests but do zs at every socket outlet. Who does do the 3 step test on an eicr?
Completely agree.An EICR is a "snap shot" of a installation this is NICEIC's view, i spend about 5 full working days a year on site with them and constant review of jobs and certificates.
The less you take apart the better, you more likely to cause a fault. A good tester should be able to use there skill and judgment on just how much needs opening up. The numbers and readings are just a small part of a EICR.