Hi , Can anyone help.
Got an electric roller door , the door motor has been hit by a forklift truck and has damaged the wiring to the motor. The motor has no terminal box , the terminal cables just come off the windings directly. I have dissasembled the motor and found only w1,w2 winding still connected , i found this coil to have a resistance of 9 ohms. The other 4 wires (u1,u2,v1,v2) were all ripped out. however using my meter i found the other two coils (measured at 9 ohms) and reconnected the wires.

So in short i have three coils,u1-u2 , v1-v2 and w1-w2 all with 9 ohm resistance , however if i test between u1-v1,v1-w1 or w1-u1 i also get a reading of 36 ohms (i would have expected this to be a megaohm reading).

Anyhow , i have reconnected the motor but when i press the control for up and down the motor always goes in the same direction !

Is there anything i can have got wrong on the motor wiring or is there something wrong with the control ?

Any help is very much appreciated.
 
The motor must be supplied from a control box that contains contactors. Check if any contactors are welded in the closed position. The answer to your problem will probably lie in that control box somewhere.
 
As Marvo said: Quite likely blown the contactor / controller.
 
Last edited by a moderator:
The fact you’re getting a reading between U1, V1, W1 would indicate some damage to the windings. The resistance is to high for it to be a reading of a star connection. I would suggest a new motor and protect it from the FLT. (Or shoot the driver).
 
  • Like
Reactions: 1 person
Thanks Tony: Think I need new eyes, just re-read the OP's post & saw the bit about winding resistances. My excuse is age & i'm sticking to it Lol.:wheelchair:
 
...the terminal cables just come off the windings directly. I have dissasembled the motor and found only w1,w2 winding still connected , i found this coil to have a resistance of 9 ohms. The other 4 wires (u1,u2,v1,v2) were all ripped out. however using my meter i found the other two coils (measured at 9 ohms) and reconnected the wires.

So in short i have three coils,u1-u2 , v1-v2 and w1-w2 all with 9 ohm resistance , however if i test between u1-v1,v1-w1 or w1-u1 i also get a reading of 36 ohms (i would have expected this to be a megaohm reading).

Anyhow , i have reconnected the motor but when i press the control for up and down the motor always goes in the same direction !

Your reconnected coils; are they correct polarity now?

A useful test if required: View attachment Motor tails identification.pdf Try this first if you can.


You say the motor is working, so not tripping and not running long enough for overload, etc...

Are we to take it there's seven wires up to the motor (U1/2, V1/2, W1/2 and E) from the control box?

Is the direction control via reversing contactor?

Is the motor noisy?

Any motor data ie. star or delta?
 
  • Like
Reactions: 2 people
Have a look in the “electrical therory” thread in the stickys. I posted a method for testing the polarity of motor windings. But with the readings you give for the inter-winding resistance I’m still favouring a short in the windings.
 
  • Like
Reactions: 1 person
So in short i have three coils,u1-u2 , v1-v2 and w1-w2 all with 9 ohm resistance , however if i test between u1-v1,v1-w1 or w1-u1 i also get a reading of 36 ohms (i would have expected this to be a megaohm reading).

I can't fathom how you get 36 ohms! I can get near 3.6 ohms as a delta connection. Where were you measuring this 36 ohms and was it identical for each of the three tests? Were the wires open?

Any chance of it being a two speed motor?
Is it one of them high speed doors?
What is the manufacture and model?

What do you measure between U2 and W2? 18 ohms?
 
Last edited by a moderator:
yous are good, how you know resistances of a coil.. im sure in time il be up there but for now how.
 
  • Like
Reactions: 1 person
I get 6 Ώ. for delta. This is a purely resistive test so phase angles have no effect.

Rt = 1/((1/R1)+(1/R2))
where R1 = one winding
R2 = two windings in series.


Rt = 1/((1/9)+(1/18)) = 6Ώ

View attachment 9071
 
Last edited by a moderator:
  • Like
Reactions: 1 person
@Tony...... you seem to have deep down hatred of folk lift drivers lol can you enlighten us?
I partly rely on crap folklift driver to pay my wages they are a regular income for me so cant be shooting them more like ...Get that man a beer!:chillpill:
 
I’ve spent to much time repairing what they’ve destroyed. Walls demolished, pity about the distribution boards on the other side of it, the list is endless! As for roller shutter doors, I’ve lost count of the number wrapped around the mast.

BTW I hold a FLT licence.
 
  • Like
Reactions: 2 people
Ok , an update on this , i have an identical door and have removed the motor from it to fit to the door with the problem. I have wired the 6 wires from the new motor exactly as the old motor was wired in the terminal box.
There are 3 contactors only in the panel , k1,k2 and k3. Looking at the 'working door' before removing the motor , when the door is selected down , only k2 comes in , when selected up k1 and k2 come in together. The motor is Electromaten SI4/8.85/165.35,00 which i now believe to be a two speed motor.The outgoing side of k3 has its three terminals all linked together. The door should operate upwards at full speed and downwards at a lower speed hence two contactors are in on the way up. Now i have simply replaced the motor onto the 6 original terminals and the motor goes downwards (close) regardless of wether i press in k1 or k2. if i press k1 and k3 (up) then the motor buzzers as if it is stalling. I cannot see what is wrong now the motor has been replaced (knowing it is a good motor).
Anyone help ?
 
If you've replaced the motor with an identical motor & connected it up properly then what do you have left ?: Wiring, Contactor / Controller.
As has been said previously it's quite likely that when the motor wiring was ripped out it killed the contactor.
 
Last edited by a moderator:


Any chance of it being a two speed motor?
Is it one of them high speed doors?
What is the manufacture and model?

What do you measure between U2 and W2? 18 ohms?

whitebeetle; said:
There are 3 contactors only in the panel , k1,k2 and k3. Looking at the 'working door' before removing the motor , when the door is selected down , only k2 comes in , when selected up k1 and k2 come in together. The motor is Electromaten SI4/8.85/165.35,00 which i now believe to be a two speed motor.

The outgoing side of k3 has its three terminals all linked together. The door should operate upwards at full speed and downwards at a lower speed hence two contactors are in on the way up.

Now i have simply replaced the motor onto the 6 original terminals and the motor goes downwards (close) regardless of wether i press in k1 or k2. if i press k1 and k3 (up) then the motor buzzers as if it is stalling. I cannot see what is wrong now the motor has been replaced (knowing it is a good motor).
Anyone help ?

TwoSpeed.jpg


http://www.wiringmanual.com/motor052.html
- start with this info.

Low speed = supply via K2 to U1, V1 and W1 with UVW2 open.
High speed = supply via K1 to U2, V2 and W2 with UVW1 shorted or starred in K3.

Does the supply for the motor come from a dedicated board with plug in connections?

What resistances did you measure with the 'replacement' motor windings?
 
Last edited by a moderator:
  • Like
Reactions: 1 person
Hi , Many Thanks.
The supply to the motor comes from a circuit board with screw terminals where the motor wires go. The door is manufactured by Crawford and is a high speed door , i am not sure of the model as there is no more info on it.
Thanks again for your help.
 
Thanks for coming back with info. The more you give the better the help...well, that's the aim!

This subject is not really something I'm familiar on but we'll get there.

Any of these? High speed doors for fast action

On the original motor the direction didn't change. This time its doing the same but in the other direction. Try interchanging UVW1 with UVW2 and also two wires to the up side of the motor in order to change DoR.

If it continues to run in only one direction then perhaps something else is sending it in that direction, any chance the control board decides the direction?

Definitely check the contact continuity of each of the contactors K1 and K2!
 
Last edited by a moderator:
It can't be connected correctly.
It sounds as if you need to swop over two of the conductors connected to one of the up contactors.
You say that when you press in K1 and K3 together, the motor just buzzes.
This would suggest that one contactor is attempting to drive the motor in one direction, and the other contactor in the other direction.
As both K1 and K2 drive the motor in the same direction, and when K1 and K3 are pressed together the motor buzzes, I would suggest swopping round the conductors connected to K1, so that when K1 is pressed the motor direction is reversed.
I don't understand why when up is selected K2 operates, to my mind it should be k1 and k3 together for up and K2 on it's own for down.
 
Did you have a look at the web site I posted? There are three ways of connecting these motors. If you are using reversing you need four contactors.

From experience I can tell you they are swine’s when they go wrong. We used them as reversing constant torque on a crane. Your using the variable torque connection.
 
If you are using reversing you need four contactors.

This is why I asked if the control board could reverse a phase, as the OP said the motor supply comes off this board.

The other thought... as this motor turns one way in high speed (UP) and one way in low speed (DN) then can the motor be wired with lines interchanged on one side of windings?

I've not done much with two-speed motors other than dahlanders on Baltimore Air Coils, almost 10 years ago. Inverters have boomed during these last sixteen years of my learning!

.
 
  • Like
Reactions: 1 person
Now you're asking! Will have a look in to it. It's like opening the doors to a long locked room. My brains creaking.
 
can you post me a picture of the motor and starter panel and chech if theres and safety devices on the door ive been workin on industrial doors for the past 11 years and crawfords are the most problematic as they are designed to go wrong and getting spare parts off them is nearly impossible
 
Been asked to recommision a campisa door today by the plant manager. I've done as requested and it works for now. But this reverses off the board and I've had similar confusing faults. I think, Tony has said, don't get to bogged down with testing. get more involved with how it should function.

As jonesy has said, I worked on this door for nine years and its garbage. We've since had a door, I assume we are talking about fast acting doors, from fenbay services and its, over the year been excellent.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Electric roller door motor help.
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
whitebeetle,
Last reply from
sbrown2,
Replies
29
Views
6,627

Advert