Hi everyone
Need help pls I have installed cooker circuit using 6mm twin earth with 45amp switch

The hob is 6kw
My question is what size flex do I use to connect from cooker outlet to hob
6mm is way too thick to connect to terminals and hard to close the cover

The paper work for the hob say
Use 3 core 2.5mm

Pls help 🙏
 
If the manufacturer's instructions say 2.5mm2, then that's what you should use. HO5RN-F is good for 25A, and 6kW at 230V is just over 26A, but that's before any diversity.
The problem with these imported things are that they are designed for three phase supplies, and converted to single phase for the UK market by including some links for the terminals. The three phase cable would be ore than adequate at 1.5mm2, so that's what the terminal box is designed for.
 
If the manufacturer's instructions say 2.5mm2, then that's what you should use. HO5RN-F is good for 25A, and 6kW at 230V is just over 26A, but that's before any diversity.
The problem with these imported things are that they are designed for three phase supplies, and converted to single phase for the UK market by including some links for the terminals. The three phase cable would be ore than adequate at 1.5mm2, so that's what the terminal box is designed for.
Thank you very much for your reply
If the manufacturer's instructions say 2.5mm2, then that's what you should use. HO5RN-F is good for 25A, and 6kW at 230V is just over 26A, but that's before any diversity.
The problem with these imported things are that they are designed for three phase supplies, and converted to single phase for the UK market by including some links for the terminals. The three phase cable would be ore than adequate at 1.5mm2, so that's what the terminal box is designed for.
Thank you for the reply 🙏
 
H07RN-F is typically rated to 60C which is often fine and good to work with.
BS6004 "Arctic" cable is 70C but usually reels of 50m or 100m.
3183B flex is similar 70C limit but sold by the meter (e.g. Superlec 3 CORE 2.5MM 3183B (H05ZIZI-F) ZERO HALOGEN FLEXIBLE CORD - https://www.superlecdirect.com/cables-and-accessories-c1/ho5z1z1f-318b-cable-s241000005/p-3183b2.5-superlec-3-core-25mm-3183b-h05zizif-zero-halogen-flexible-cord/)
6242B LSZH T&E is rated to 90C (which often surprised folks) so sometimes a choice for cookers where terminals get hot.
3183TQ is also rated at 90C but usually on reels as well, but bizarrely Screwfix sell 1m lengths! (Time 3183TQ White 3-Core 2.5mm² Flexible Cable 1m Coil - https://www.NoLinkingToThis/p/time-3183tq-white-3-core-2-5mm-flexible-cable-1m-coil/71940)
 

Reply to Electrical hob 6kw how to connect in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K
Another hob wiring question sorry, I am replacing my oven and hob and the oven connections was fine, 6mm from new consumer unit on a 32a RCBO...
Replies
4
Views
3K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
628
Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
788

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock