Discuss Electrics to new wooden 'man cave' 10 m away from house in the UK Electrical Forum area at ElectriciansForums.net
Leeds2020
Hello, I need some electrics to my new wooden man cave. It is 10 m away from the house, I need need lights and sockets for the fridge and electric heater. I have no space in consumer unit but two ring mains down stairs (kitchen and then all other rooms) onto 32 amp MCB's.
I have been told that a 2.5mm armoured cable, 600mm in ground, added to the kitchen ring main will be OK? I also intend to put a small consumer unit inside the 'man cave to feed from for all sockets and lights. Is this good advice?
No, I’d not be doing it like that. I’d split the tails at the origin into a switched fuse, then run an appropriately sized SWA to the shed and into the CU before adding any final circuits required. I’d also be taking into account max demand, type of earthing, voltage drop, EFLI, bonding requirements etc.... The list goes on.
Do yourself a favour and get a sparky in.
What he said, wouldn't be much more expensive to do it properly.
What you are initially proposing, to take a spur off the ring final to the outbuilding would be OK if it was limited to 13A. So a FCU (fused connection unit) is added to the ring and that feeds your 2.5mm cable and then in the out-building you can have sockets and another FCU with 3A fuse to switch/protect the lights circuit.
But if you need more than 13A, which if you want a 3kW heater and a fridge kicking in at 5A+ every so often it looks like it, then you need really to go with #2 post by @JBW175 suggestion and get in a dedicated new supply. If that is too expensive, then look at limiting your heater to 1-2kW max.
Speak to a local electrician (one who is registered with one of the competent person schemes like NICEIC/SELECT/etc) about it, they are probably happy for you to put in the armoured cable so long as they type/supplier is one they know and trust.
2.5mm is really only OK for 20A or so which should be fine here, but is too much to be taken off a single point of the ring final. But for all the extra cost of the cable, if it is going in as a dedicated feed then you might want to get it sized for more so you can have stuff in the future like a big hot-tub, or car charger, etc, depending on the garden layout, etc.
Also you really want them separate from your house sockets, either dedicated feed or a double-pole isolating FCU, so in the event of a fault you can isolate the out building and restore your home electrics until such point when it is fixed. As it will most likely be middle winter and pouring down rain, etc at the time!
Reply to Electrics to new wooden 'man cave' 10 m away from house in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...