Discuss External earth fault loop impedance Ze in the Industrial Electricians' Talk area at ElectriciansForums.net
V
voltage
Hi all
Just checking this procedure is correct for Ze
This is a live test so with the consumer unti front off i would lock off main switch keep RCDs on and all MCBs on.
Dissconnect the main earth.
Now on the megger 1553 i would set it to no trip and use the 3 lead method ?
So green lead croc clipped to main earth
then using the red lead as a probe put this on line
and using the black lead as a probe put this on neutral
then take the reading ? repaeat test for good practice record result then reconnect main earth ?
is this the correct procedure on how you would carry out this test ?
many thanks volt.
It can also be done with just 2 leads (without the neutral as long as you are before any rcd) - clever things these meggers :)
ahh right well i will be before any RCD so
so what setting would the megger need to be on ? Hi loop ?
Then use green lead with croc clip on for main earth
Then use red lead as probe for live
test
then repeat putting red probe on neutral and test ?
The setup on consumer unit is main switch 100amp then RCD then 4 MCBs spare way then second RCD then 3 MCBs then 2 spare ways.
test
not the highlighted bit.
voltage, you've got it , by jove. 2 lead or 3 lead on hi. don't forget though that the next test, for pfc requires the eart lead to be reconnected.
Reply to External earth fault loop impedance Ze in the Industrial Electricians' Talk area at ElectriciansForums.net
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Can someone explain this to me? The regs book calls Zs 'Earth Fault Loop Impedence' and the On-Site Guide calls Ze 'Earth Fault Loop Impedence'.
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...