robinsmith30

This is my first post to seek advice from experts as a non-electrician, as to whether what I am being told is correct.

We have recently been supplied an Xplelair inline extractor fan with timer in our bathroom. The electrician fitted it such that when the bathroom light is switched off, the fan switches off. We have asked for this to be changed such that the timer can be used (i.e. the fan switches off 10 minutes after the light is switched off). We have been told that the fan needs to rewired to do this at our cost.

This sounds a bit suspicious to me. Does such a change typically need re-wiring?

I’ve done a little research, and there only seems to be one wiring diagram shown http://www.taps4less.com/pdf/Xpelair-Axial-Inline-Shower-Fan.pdf
However, I’m not an electrician, so seek advice if anyone knows whether the electricians position is reasonable.
Kind regards,

Robin
 
It all depends on what cables go to the fan very hard to answer without more info

why are you getting an electrician that you don't trust to do your work??
Or why are people always suspicious of electricians???
 
This is my first post to seek advice from experts as a non-electrician, as to whether what I am being told is correct.

We have recently been supplied an Xplelair inline extractor fan with timer in our bathroom. The electrician fitted it such that when the bathroom light is switched off, the fan switches off. We have asked for this to be changed such that the timer can be used (i.e. the fan switches off 10 minutes after the light is switched off). We have been told that the fan needs to rewired to do this at our cost.

This sounds a bit suspicious to me. Does such a change typically need re-wiring?

I’ve done a little research, and there only seems to be one wiring diagram shown http://www.taps4less.com/pdf/Xpelair-Axial-Inline-Shower-Fan.pdf
However, I’m not an electrician, so seek advice if anyone knows whether the electricians position is reasonable.
Kind regards,

Robin

What makes you think you have the timer version? There are a number of versions of the fan.
 
Hi guys,

Thank you for your prompt response. The reason I think I have the timer version, and the reason I am suspicious is that the written quote lists the following line item
1 Xpelair Fan White
Xplelair Inline Extractor Fan with Timer
So I think it is reasonable to ask the question :)
 
You will note on the link you give that there are two wiring diagrams shown on page 3, the top one is for non timer fan and the bottom one for the timer fan.
The timer fan would need a permanent line and if that was not installed at the time then it would need a new cable.
If you agreed originally to have just an on off fan in line with the light and the electrician did this, he would not have needed to supply a permanent line.
 
Hi guys,

Thank you for your prompt response. The reason I think I have the timer version, and the reason I am suspicious is that the written quote lists the following line item
1 Xpelair Fan White
Xplelair Inline Extractor Fan with Timer
So I think it is reasonable to ask the question :)

Can you easily access the fan and see what the model number is? Maybe they bought the wrong one!
 
Thank you for the follow up questions. Our specification detailed Xplelair Inline Extractor Fan with Timer. The electrician has not told us they have fitted the wrong fan, they have said they need to re-wire the existing fan (at our cost) to make the fan timer work.
 
Thank you for the follow up questions. Our specification detailed Xplelair Inline Extractor Fan with Timer. The electrician has not told us they have fitted the wrong fan, they have said they need to re-wire the existing fan (at our cost) to make the fan timer work.

If they have quote and invoiced for a timer with fan, and it doesn't operate with a timer over run, then they need to come back and rectify the situation at THEIR cost. IMHO
 
Extractor fan – Is a re-wire change to change timer duration?

If your sparks has quoted for a timer fan I would have liked to think that he had looked at the wiring first. Did he?

You need three cable for a timer fan, permanent live, neutral, and switch live from light. If the existing wiring doesn't have this then the fan will only come on and off with the light.

I bet he didn't check the wiring first. But either way if he had and it wasn't correct, and you wanted the timer fan, then he would still have to rewire this cable. So you would still have to pay for it.
 
This was an installation of a brand new en-suite which included new lights and "Xplelair Inline Extractor Fan with Timer". The functionality we now have is not in line with the quotation. So if the electrician has wired it up in way in which the timer does not work, is this our fault? We don't see why we should pay for this to be rectified. This has only come to light as immediately after fitting we asked for timer to be adjusted.
 
all bolis down to what was quoted for by the spark. if he had quoted to fit a timer overrun fan, then it's his problem if he's not wired it correctly. if he quoted just to fit the fan to run with the light, then it's your responsibility to pay for the extra wiring involved.
 
Extractor fan – Is a re-wire change to change timer duration?

Oh oh oh. Sorry I didn't realise he had done all the wiring. If he's wired all the lights and a new feed to a fan then he is totally in the wrong.

Get him back. If he doesn't come back, complain to his registration body and they will make him.

Apologies for my assumptions.
 
This was an installation of a brand new en-suite which included new lights and "Xplelair Inline Extractor Fan with Timer". The functionality we now have is not in line with the quotation. So if the electrician has wired it up in way in which the timer does not work, is this our fault? We don't see why we should pay for this to be rectified. This has only come to light as immediately after fitting we asked for timer to be adjusted.

You have now give more info and your op now makes sense. It seems that the spark has not wired it for a timer fan. IMHO it's his problem
 
This was an installation of a brand new en-suite which included new lights and "Xplelair Inline Extractor Fan with Timer". The functionality we now have is not in line with the quotation. So if the electrician has wired it up in way in which the timer does not work, is this our fault? We don't see why we should pay for this to be rectified. This has only come to light as immediately after fitting we asked for timer to be adjusted.

Sounds like hes lashed in a twin, and ran away.

Few other things to ponder,,

Fan isolation switch,is the fan protected by a fuse or does it have thermal cutout on it, where you issued a certificate for your electrical work done lights and fan, are your lights compliant to the bathroom zones.

Not trying to make a mountain out of it, but these things need to to be looked into, by any electrician worth his salt.
 
Not wanting to be funny but why would you specify the ventilation - are you a ventilation expert - only jesting ...... it seems easy until you know the truth !

The link is to an Axial fan - i hope there isn't too much ducting as it may not perform if too much.

There are a lot of different things to take into account in selecting the best ventilation solution, you could see Energy Savings trust web site, or study the downloadable Domestic Ventilation Compliance Guide along with Part F of the Building Regulations.

It sounds like you've got a system 1 type installation, For these systems " when installing a fan within a bathroom or wc with no openable window the fan should have a 15 minute over run " and " in rooms with no natural light, the fan should be controlled by the operation of the main light switch within the room."

Is your bathroom door undercut by 10mm above carpet or other finish ?

Has the room got a window ?

Flexi duct used or rigid ?

Generally point of extract should be as far from the internal door as possible to achieve best ventilation, however that may mean you get a short circuit to a window background ventilator (if fitted) or you may just go for above the shower ?

All that said i am teasing a bit - ventilation on new build is now a controlled service and when you see how many installations are actually poorly installed you can see why. How many electricians have an air flow meter to ensure the fan performs ?

PM me with as much detail about job inc sketch of room layout etc and i can provide best solution.
 
Last edited by a moderator:
Not wanting to be funny but why would you specify the ventilation - are you a ventilation expert - only jesting ...... it seems easy until you know the truth !

The link is to an Axial fan - i hope there isn't too much ducting as it may not perform if too much.

There are a lot of different things to take into account in selecting the best ventilation solution, you could see Energy Savings trust web site, or study the downloadable Domestic Ventilation Compliance Guide along with Part F of the Building Regulations.

It sounds like you've got a system 1 type installation, For these systems " when installing a fan within a bathroom or wc with no openable window the fan should " and " in rooms with no natural light, the fan should be controlled by the operation of the main light switch within the room."

Is your bathroom door undercut by 10mm above carpet or other finish ?

Has the room got a window ?

Flexi duct used or rigid ?

Generally point of extract should be as far from the internal door as possible to achieve best ventilation, however that may mean you get a short circuit to a window background ventilator (if fitted) or you may just go for above the shower ?

All that said i am teasing a bit - ventilation on new build is now a controlled service and when you see how many installations are actually poorly installed you can see why. How many electricians have an air flow meter to ensure the fan performs ?

PM me with as much detail about job inc sketch of room layout etc and i can provide best solution.

Bloody hell!!
It's Friday you know! Go grab a pint and relax!
 
Thank you for all the responses. I have a couple of final questions to help clarify my understanding 1) Can a fan with a timer be set to a time of 0 and 2) When installing a fan with a timer, is the wiring the same regardless of the timing being set to 0 or maximum. We are awaiting our certificates for the work. I will check on the matters raised by Toonlad in due course.
 

Reply to Extractor fan – Is a re-wire change to change timer duration? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
359
This weekend we are offering up to 42% off some of our best-selling silent + timer extractor fans. Hurry as these prices are available for this...
Replies
0
Views
308
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
11
Views
331
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
232
Good afternoon everyone. I have fitted an extractor fan in my bathroom with an overrun timer, to start when the bathroom led lights are turned on...
Replies
92
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock