Hi all,

I'm a newby and seeking some advice.

My aim is to add a socket (power source to run led lights -12v transformer) from the existing single socket. The socket in place comes off a single cable out of the wall to a fused spur (and then to the socket).

I am unsure if I have a ring or radial circuit.

Reading up suggests this is straight forward and that either a radial or ring setup allows me to extend off the fused spur with 2.5 cable.

Can anyone see any problems.


Thanks in advance.
 
You can have as many sockets as you like AFTER the fused connection unit. Just make sure total load on all sockets will be less than 13 amps! The only considerations are Zs and voltage drop, not usually an issue if the cable runs are quite short.

To be absolutely sure, you'd be best to get a spark in, wouldn't cost that much.
 
Last edited:
but if the circuit is a radial, there's no need for fusing down, providing that the OPCD in the CU is the correct rating for the radial circuit.
 
but if the circuit is a radial, there's no need for fusing down, providing that the OPCD in the CU is the correct rating for the radial circuit.

Very true. But if it's a 4mm 32a radial, and the cable after the the fused spur is 2.5mm, fusing down would be necessary. Didn't go into such detail as from the OP the FCU is already in place.
 
agreed. ^^^. too early in the morning after for me to have thought about the 4mm.LOL.
 
I am unsure if I have a ring or radial circuit.
.

I would need to know myself regardless, get your continuity tester out and test it, I bet you would love to know though Right? you would wouldn't you? what size MCB or fuse is protecting the current circuit? how big is the existing circuit? whats connected to it? Just questions I like to know before adding anything further to existing cabling.

Welcome aboard by the way
 

Reply to Fused spur in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
662
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
389
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
178
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock