I shall be replacing my dual RCD CU, for a all RCBO populated CU. A question or two about technique for IR testing.

For the IR test, I've read here before that a global IR test is preferable. With older types of RCBO's that wasn't possible, without disconnecting cables, which ended up with the testing of each individual circuit.

I'm installing a Hager CU, with their miniature ADA RCBO. The MI state an IR test can be carried out on the RCBO terminals, circuit connected with the RCBO turned off. As I've a few different sorts of luminaire connected, I will be doing live/neutral to to earth.

How do you carry out such a test? I've seen some stackable MFT leads, so you can combine live & neutral together?
 
Just disconnect the circuit conductors, whack them in a Wago with a fly lead and test between the fly lead and the earth bar. Or use a jumper cable if you want to be sure (I have a set of Kewtech leads that are stackable or that can take a croc clip on each end). but for the most part I put one lead on the earth bar with a croc clip and then put the other conductors in the other croc clip.

But, I would definitely not be test from the RCBO terminals. The neutral fly leads can cause issues, as can functional earths. So, yes... pain in the posterior, but I disconnect the circuit under test and take it from there.
 
A global IR test is done with the main switch in the open position and all the final circuits in parallel, mcb’s closed, not possible to do with all ocpd’s being rcbos.

Hager rcbos allow for IR test at their terminals as it’s stated on the device, with obviously the ocpd in the open position
 
Look out for RCBO with functional earths as they show up when doing global or L+N to E testing. The Hager commercial RCBO have them but I don't know about the domestic ones.
 
A global IR test is done with the main switch in the open position and all the final circuits in parallel, mcb’s closed, not possible to do with all ocpd’s being rcbos.

Hager rcbos allow for IR test at their terminals as it’s stated on the device, with obviously the ocpd in the open position
I've seen those stackable leads, so at least your testing circuit live against all neutrals, but I guess its just testing one circuit at a time really.
 
Look out for RCBO with functional earths as they show up when doing global or L+N to E testing. The Hager commercial RCBO have them but I don't know about the domestic ones.
The newer Hager miniature RCBO's, doesn't have a functional earth. One less thing I guess.
 
The most searching test. more so than a global test, is to test the circuits individually with all other conductors earthed. With DP switching in RCBOs, that's easy to achieve. Lock off the main switch and link the line, neutral and earth busbars in the CU together (preferably connect to the line busbar via an MCB to avoid blowing the DNO fuse if the link is accidentally left in when re-energised).

Then flip off each RCBO in turn, test the circuit at its outgoing terminals , flip it back on and move to the next circuit.
 
The most searching test. more so than a global test, is to test the circuits individually with all other conductors earthed. With DP switching in RCBOs, that's easy to achieve. Lock off the main switch and link the line, neutral and earth busbars in the CU together (preferably connect to the line busbar via an MCB to avoid blowing the DNO fuse if the link is accidentally left in when re-energised).

Then flip off each RCBO in turn, test the circuit at its outgoing terminals , flip it back on and move to the next circuit.
The Hager ADA aren't DP (or switched neutral), so not an option for me.
 
Because these RCBOs have no functional earth connection, if you are only testing from (L+N paralleled) to earth I think you're good go with a global test. With all RCBOs on, all terminals of each RCBO are connected together, so they cannot influence the test nor are they subjected in any way to test voltage.
 
Because these RCBOs have no functional earth connection, if you are only testing from (L+N paralleled) to earth I think you're good go with a global test. With all RCBOs on, all terminals of each RCBO are connected together, so they cannot influence the test nor are they subjected in any way to test voltage.
The MI say to test from the load terminals, with the RCBO in the 'off' position. Too frightened to turn them 'on'. ?
 
I was looking at that marking on the Hager ADA RCBO's last week and thinking it doesn't really help all that much as they don't have a switched neutral. Very annoying they didn't incorporate this when designing the RCBO a couple of years ago.
 
The only problem with switched neutral RCBO's is they are dual module, not a problem in a continental type CU but very restrictive in a normal UK domestic board, I had to use single module RCBO's for the lighting circuits due to lack of room.

 
The only problem with switched neutral RCBO's is they are dual module, not a problem in a continental type CU but very restrictive in a normal UK domestic board, I had to use single module RCBO's for the lighting circuits due to lack of room.

I’ve installed another CU in my garage, that Wylex NM with switched neutral RCBO’s.
 
I would like to believe that, but the neutral from the circuit is still attached to the connector block in the CU and therefore has not been isolated. It can't isolate the neutral if the circuit does not pass through the RCBO or have a missed something here?
 
I always use dual module rcbo, s (Hagar or GE) where space allows. Single module only where space restricted. A CU with dual module rcbo, s is the easiest CU to install that has ever been invented. The dual module buzz bar means no neutral fly leads. A joy to work with.

Not readily available here in England.
 

Reply to Global IR testing on RCBO populated CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Did a check on a ring circuit, due to board having to remain live I did it at a socket.. Was an RCBO, had checked RCD side and all tested ok...
Replies
3
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock