David M

-
Esteemed
Reaction score
634
So I was called out to a faulty light today. turned out it was just a loose connection.

Anyway it got me thinking about poor termination procedures when fixing back accessories. One of the first things I taught my previous apprentice about installing items was to check for loose connections before fixing back. What had surprised me at the time was that he was never taught or shown at college how to ensure he had prevented a possible loose connection.

As an example after I've terminated a socket outlet I gently and neatly fold back the cables and push the face plate into position making sure that no wires are trapped. I then ease the face plate forward just enough to check the termination screws for tightness before fixing the plate back. Often you find that one or more of the terminals have loosened due to the movement of the wires as you locate the face plate. I do this with every single accessory I install. I check every terminal for tightness on all and any item before I replace the lid or cover. Now I assume you guys do pretty much the same. :)

What had surprised me was my apprentice whilst in college was never taught to follow this or a similar procedure. The baffling part is, there is so much concern (rightly so) about potentially dangerous hazards which could result in fires, electric shocks and so forth, yet something as basic as teaching first year apprentices how to ensure good connections is overlooked?? :thinking:

It could be that this particular lecturer during the practicals had missed this crucial lesson. But if it is a nation wide problem do you think it needs addressing or am I just over reacting? (little touchy today):baby:
 
Last edited:
Removing and old consumer unit yesterday, I'd say 90% of the terminals were loose. I also found the shower neutral had been loose too (pic). There was also no continuity on r1 and r2 of the ring circuit, upon removing two items in the kitchen, the lives had both dropped out of the terminals.
So no, I don't think you are over-reacting.
1.jpg
 
I had an argument at ELEX last year in Coventry about this very issue, pointed out that IMO most of the blame was at the feet of the trainee establishments, not all of them I hasten to add, this argument stemmed from a discussion about the spate of fires in consumers units, got a bit of a cold reaction from most of the cast, I can only think they were protecting their own backs, this is how I perceived the discussion, I could be wrong, but my gut feeling, well better not go into that for fear of a backlash. That's my take on the issue for what it's worth.
 
strange that 99% of these CU fires have occurred since the advent of Electrical Trainee training courses, virtually none in the last 40 years of plastic CUs. draw you own conclusions. as in post#1, recheck connections, after a wiggle. 90% of the time tails will need a turn or more after a good wiggle. how many Electrical Trainee's are taught this?
 
I think there's a strong case for making thermal imaging and visual checking a regular requirement. Thermal imaging equipment is now at the point where the price is accessible for most small businesses and it's very effective when it comes to highlighting high resistance terminations.
 
I just installed 15 x 6way boards in bedsits, 90% of the main RCD outgoing terminals were onto the busbar and N link were loose - its down to people not checking properly before energising and putting into use that we see these fires and a large part of the reason the ammendment 3 changed the board construct, if this was driven hard into trainee's rather than a casual mention then there wouldn't have so many burn outs and overheating that I have witnessed has increased significantly over the last few decades... mass manufactured cheap crap also lends itself to the problem and allowing DIY stores to sell consumer units etc to Joe public even though they should not actual change it themselves - if we have issues we trainee's and Electricians not checking the terminals, what can we expect of a DIYer.
 
Last edited:
Point taken, of course human error will come into it, always give the pull test, but some products are rubbish, take the 2poll isolator, no brand mentioned, single pinch spade connection you can tighten them up fully, pull and wiggle it will fall out, I strip the cable say 25mm tail, then flatten it out, it does not move, keep it circumferential it will drop out. Just a Little tip.
 
strange that 99% of these CU fires have occurred since the advent of Electrical Trainee training courses, virtually none in the last 40 years of plastic CUs. draw you own conclusions. as in post#1, recheck connections, after a wiggle. 90% of the time tails will need a turn or more after a good wiggle. how many Electrical Trainee's are taught this?

I agree wholeheartedly with Tel on this, this was the focal point of my argument/discussion with the panel at ELEX think they must have been scripted on their replies, in fact I'm sure of it
 
Poor quality products are a problem but you would hope that would put sparks on their guard and focus their minds on making the best connection possible with the available materials. Back in the day, one of the main craft skills that was considered crucial for every electrician was how to make sound connections. From sweating on lugs to making tensile inline splices (and insulating them), it was one of the fundamentals of the job. Woe betide the lad whose instructor found he hadn't bent up the ends of his Britannia joint square before soldering! Granted, no-one really needs to know how to vulcanise a rubber joint or sweat a lead octopus any more but things have gone too far the other way - newbies waxing lyrical about torque gauges etc and bandying reg numbers about but given a screwdriver and a piece of choc block they can't get current to flow from one cable to another without catching fire. Poor show, I call it.
/rant.
 
Last edited:
One of the problems is the lack of understanding of the potential danger and risk such a poor connection can create over time. One guy once said to me that he doesn't worry about his terminations as when he tests it will show up. What about terminations you don't test? Or those you just assume are tight like in cu's as mentioned in this thread. What a cowboy!

Yeah sure when testing some circuits a poor connection may show in the readings but we all know that in a new install you can still get a compliable resistance reading even with a loose connection because the copper is clean and most likely in contact with a clean brass terminal. But over time during use this poor termination deteriorates and that resistance soon increases thus creating a potentially dangerous hazard.

You'd be surprised how many trainees and some electricians I've met who don't understand this. Or rather don't concern themselves with it, or don't see the issue until you point out the potential danger it can create.
 
Last edited:
Further to the above; how many terminals are actually brass nowadays and not just brass plated, or even just brass coloured ?
Remember when the strip of metal joining the two "screw-hole earths", across the rear of a socket was actually copper?
 
Good point.

I did a job two years ago where working on one circuit in a CU I routinely checked the connectors on the other MCB’s to find 6 were loose including the two pictured below. The two lighting circuits had presumably been forgotten completely and since I was the first person to work on the CU since the occupiers moved in 5 years previously they were very luck not to have had a problem.
Some people are just careless.

20140904_130739.jpg

20140904_130739.jpg
 
TBH the London centric AMD 3 regs have highlighted a problem that the IET and industry parasites have chosen to regulate rather than address the root cause.
When all said and done all the CU's I've fitted in the last God knows how many years have all come with a note to check the integrity of the factory made connection and they almost a!ways need tightening, so much these days is built to a price which will always involve compromise somewhere but why do CU,s in London more frequently cause fires than anywhere else in the UK
Training has been an issue for many years now but there is only so much you can fit into 17 days or 5 weeks there needs to be a major review of not only training but the experience needed to achieve competence to be qualified even now some 35+ years after finishing my apprenticeship I still draw on things learned way back then
Torque screwdrivers and anything else they care to suggest have limitations in the quality of the the finished job if people choose to blindly follow the recommendations of people who appear to have little real world industry knowledge yet set the standards by which we have to abide how can we ever expect any changes to happen to improve the situation we are currently in
 
Think it's a combination of all those things mentioned, skills, training & quality of the product. It would of been fascinating to see the investigation process of fires investigated by the LFB, but I guess it stops at the point where the source of fire is found, nothing further determined.

The schemes make a good point about lack of maintenance in domestic properties electrical installations; some times I bet I'm the first person to look inside some CU's in ten, twenty years, full of cobwebs & carp. But this only happens, when the customer wants some new work down. Cars have mot's, commercial/industry installations have maintenance plans, domestic properties should have too. Always spend 5 mins going through that CU, giving it a (quick) mot. Won't have one for another ten or twenty years, regardless of what the label says.
 
Last edited:
As above in my opinion, all three things are having an effect. As more and more cheap products come onto the market through eBay and the such things are only going to get worse. That said even the half decent product manufacturers seem to have problems, we had a faulty batch of emergency lights a while back where the push in connectors weren't grabbing the cables, the company responsible denied all knowledge saying it was how we stripped them, But out of seven sparks none of us could make them work... I think there is also an issue with a lack of space in accessories and terminations in a lot of cases.

It would be very interesting to see if there is a correlation between any electrical fires and Electrical Trainee Sparks, unfortunately I can't see any such research done as it would lead to unpleasant reading. its things like ensuring terminations are tight that I was tought by my employers and mentors as opposed to at college, where they merely touched on the subject. But I think as traditional apprenticeships seem to be dying out these things will only get worse. I for one have no idea what "Sweating a lead octopus" is lol.
 
I went to a flat to look at a lighting fault recently. The outgoing cable from the lighting mcb had burnt out completely and the mcb had melted.

So a new mcb.

Then I checked all the connections in the box which was installed 14 years ago - nearly all needed tightening

Never see this on the 30 year old units, so for me it's the quality of the parts to blame
 

Reply to Good practice - preventing loose connections in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Replies
4
Views
911
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
769
Long time no see and I hope you're all doing well. I see that torque screwdrivers have become the height of fashion in the UK over the last...
Replies
96
Views
9K
I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock