Hi guys ,

I need a little help to do a cable calculation .
I have got to install a swa cable to a new merlin gerin 8 way 3-phase d/b via a new 520/415V transformer about 70KVA with a secondary output of around 80A
The cable will be a 4 core (3 phase+earth )
The length of cable is 80 metres , 20 m of which is in a 4 inch underground duct the rest is run along a perlin on the inside of a warehouse , there are about 3 other cables run along this perlin too .
The supply voltage is 520v 3 phase+earth
63A bs88 fuses are fitted in the distribution board feeding the transformer .
From the transformer there will be again a 4 core (3 phase+neutral) with seperate earth .
The merlin D/B will be fitted in a rittal enclosure in an outside compound .
The main switch is a 125A and all circuits will be RCBO's
At present there are only going to be 4 ciruits supplying 4 portakabins for contractors .
I'm not to good with cable calculations but have tried and also taken into account the volt drop , I came up with a 25mm cable .
Please could someone tell me if I am right with my answer or if I need to alter the cable size
 
70KVA @ 415V FLC = 97.3A There’s your starting figure.

And you’ll be pushing your luck with the supply fuses 525V = 77A

 
Last edited by a moderator:
cheers tony , the fuse carriers in the supply D/B only rated at 63Amps so looks like thats going to be a non-starter .
I have a 520V supply and transforming it down to 415V , so when I am doing the eqution for the design current ( Ib ) do I divide by 520V to give me the total amount of Amps ? is it 70kva/520 =amps?
when working out the volt drop , from 25mm and over there are 3 columns r , x , z how does that fit into the equation when you are multiplying mV x Ib x length / 1000 ?
 
Last edited by a moderator:
Line Voltage / √3 gives phase voltage
KVA * 1000 / 3 / phase voltage gives current per leg of the transformer.
You have to remember there’s 3 legs each with it’s share to do.
The calculation works the same for both Delta and Star

If you PM me with your e-mail address I can send you an Excel spreadsheet for working out motor and transformer FLC’s
 

Reply to help with cable calculation in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
478
Hello all. I am in the process of refurbing my kitchen and I have and old redundant T&E cable coming out of the wall above one of the cabinets...
Replies
9
Views
2K
I'm in the process of building a new house (West Indies). Due to terrain it is a modular design where each bedroom is an individual building...
Replies
4
Views
2K
After my last post and having and having to re-learn some stuff can someone check and advise on a few things. Sorry if this is wrong don't hate...
Replies
7
Views
2K
Hi A good friend of mine is having a large electrical installation carried out in his garden.Hes had 3 prices from various electrical contractors...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock