Yes the fault affects the whole property, but you've modified one circuit. My view is the circuit is "out of normal service" during your work (including the live tests) and by testing you know it does not meet the intended design. So the circuit should not be returned to "normal service" by you.
 
  • Like
  • Agree
Reactions: DPG and westward10
LOL, What I am confused about, or perhaps, I should say, there is confusion about is; if the Ze is high, some have suggested the circuit should not be energised, but this fault would affect the entire property so would you therefor not turn off the entire installation??? Not sure how the property owner would feel about that lol.
Yes judge I was fully aware of the possible outcome of making the circuit live knowing the earth was not satisfactory.
 
Agree with all those that state advise dno to rectify but hypothetically or technically what is the difference of a tt System with zs readings sub 200 ohms?
Edit to say c/w 30ma rcd
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Hi Ze at distribution board, how would you approach?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Gringoking88,
Last reply from
Wilko,
Replies
23
Views
4,910

Advert